Does anyone have any experience with resolving an A02 fault?
"Flame present signal with burner off."
Possible cause: electrode or card fault.
It usually starts with an error code regarding no flame after ignition phase and is replaced by A02. I had a gas valve fault being displayed but got rid of it by resetting the boiler.
The boiler is 6 years old. It's not possible to use a spark tester as there is nowhere to disconnect the spark electrode. The resistance from the lead to the tip of the spark generator is 0.99 k ohms, seems high for what is just a lead? The voltage at PCB connection was 0 but is it supposed to be 240 V all the time? I inspected the gap and cleaned the tip of the electrode.
By resetting it multiple times, I managed to get the boiler to fire up and work nicely for a short time before the error came up again. Wouldn't that indicate that the spark electrode is not defective?
In fact, a few months ago I had the same issue and it disappeared until now after I reset it a few times. I had called the manufacturer then but they were not helpful other than reading the manual.