Hi there
Well after my last posts, we have a new ufh manifold and return temp is good. But we still have an issues with the water being blown out the condensate trap when the boiler starts up and melting the condensate pipe. We have a .65 80s nozzle, pump pressure 12 bar, air set to 5, co2 12.4, flue temp of 135 degrees, excess air 43%. can someone please tell me why this keeps happening. the boiler is set to 35KW. how do we get the flu temp down? thank you
Well after my last posts, we have a new ufh manifold and return temp is good. But we still have an issues with the water being blown out the condensate trap when the boiler starts up and melting the condensate pipe. We have a .65 80s nozzle, pump pressure 12 bar, air set to 5, co2 12.4, flue temp of 135 degrees, excess air 43%. can someone please tell me why this keeps happening. the boiler is set to 35KW. how do we get the flu temp down? thank you