Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Oct 9, 2021
16
3
3
England
Member Type
DIY or Homeowner
My Son has a problem with rads not getting hot and we think it may be caused by either the flow or return pipework. He has 2 rad on his living room one is hot and one is cold. Fig 1 is how the pipe work is currently, both the flow and return have tee connectors feeding the rads, the first rad is hot and the flow pipe to the second is hot but not the rad. The return pipe from the first rad is hot up to the tee and of course the return pipe from the second rad is cold. Am I correct in thinking that the flow and return pipes should be staggered as shown in fig 2 or is it only the return that this would affect as the flow does appear to be ok. Your advice would be appreciated.
Roy
 

Attachments

  • 69C78217-BC71-4C1D-9A89-D6EDD0E7363E.jpeg
    69C78217-BC71-4C1D-9A89-D6EDD0E7363E.jpeg
    344.1 KB · Views: 60
These have been added as he has had some building work. The first rad get hot but the other 2 are only warm, if that, so they are getting hot water but it appears not to be flowing.
 
Ok. It could simply be the radiators need balancing, which honestly should have been done by the installer.
What size are these radiators and the pipework feeding them? You could have an underflow proplem, or perhaps the boiler is now not man enough for the job.
First approach would be to try and balance them.
 
Ok. It could simply be the radiators need balancing, which honestly should have been done by the installer.
What size are these radiators and the pipework feeding them? You could have an underflow proplem, or perhaps the boiler is now not man enough for the job.
First approach would be to try and balance them.
Ok, I’ll try balancing the rads, the rad are tall rads about 400mm wide x 1500mm high the pipework is 15mm. I assume you don’t think it is a problem with the flow at the tee in the pipework?
 
Ok, I’ll try balancing the rads, the rad are tall rads about 400mm wide x 1500mm high the pipework is 15mm. I assume you don’t think it is a problem with the flow at the tee in the pipework?

At the moment I don't think so. It's much more likely to be a balancing issue but there are other possibilities. First try and balance the system so you have equal flow to all radiators. If you're unsure on how to do this there are discriptions on here or videos online, pretty straight forward though 👍
 
If it is all 15mm then it will work to a fashion as long as pump head sufficient except that piping is cross connected but I suppose it should be 22mm with short 15mm rad tails?.
I have two bedroom rads connected some what like that, no problems, pump head with all rads (10) in service is 3M.
 
Yeah,
At the moment I don't think so. It's much more likely to be a balancing issue but there are other possibilities. First try and balance the system so you have equal flow to all radiators. If you're unsure on how to do this there are discriptions on here or videos online, pretty straight forward though 👍
 
Ok, I’ll try balancing the rads, the rad are tall rads about 400mm wide x 1500mm high the pipework is 15mm. I assume you don’t think it is a problem with the flow at the tee in the pipework?

Ok, I’ll try balancing the rads, the rad are tall rads about 400mm wide x 1500mm high the pipework is 15mm. I assume you don’t think it is a problem with the flow at the tee in the pipework?
The tall rads (5 FT high??) are probably "1/2" the problem, are they fitted with baffles with the flow/return connected at the right ends?.
 
Maybe shut one valve on all rads except these two, ensure their valves fully open, (if downstairs can be zoned off just get this zone isolated by turning downstairs stat down) fire up the boiler and see if if the rads start heating up, even if they are being short circuited the flow and return should get hot, might tell you something.
 
Maybe shut one valve on all rads except these two, ensure their valves fully open, (if downstairs can be zoned off just get this zone isolated by turning downstairs stat down) fire up the boiler and see if if the rads start heating up, even if they are being short circuited the flow and return should get hot, might tell you something.
That’s great, thanks. I’ll give it a go.
 
Hi
I have spoken to the rad supplier and they say that the rad are not supplied with baffles and do not need them. I have returned to my Sons today and turned all the rads upstairs off, the rads downstairs heated up, I then balanced all the rads and they are now all hot as required. Many thanks for all your help.
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

C
Replies
2
Views
1K
C
Replies
3
Views
1K
UK Plumbers Forums
Deleted member 120897
D
J
Replies
2
Views
618
J

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.