H
hughs
The gas inlet working pressure in the Vaillant EcoTec plus 630 System Boiler is 16.5 mbar. The recommended pressure for this boiler is in the range 17 – 25 mbar.
The gas flow rate is 3.2 cubic metres per hr for natural gas. The recommended rate in cubic metres per hr is:
Nominal – 3.24
+5% - 3.40
-10% - 2.91
I am told that the output pressure from the gas meter is set at its maximum.
If the working pressure is very slightly less than the recommended rate, what are the implications? If I need to increase the gas pressure, what do I need to do?
Is the gas flow rate ok, noting the above readings?
Anything else that I should consider?
[FONT=&quot]Many thanks for your help.[/FONT]
Who installed this boiler and when?
Ignore that previous reply. I have looked at your other posts and it seems that this is a DIY job. You have two problems. The first is that you have a legal requirement to inform your local building control of the new installation. If this doesn't cost you now then it will when you come to sell the house. Secondly your gas supply pressure. If it is within the specs of the boiler then it is not going to adversely affect performance. If the pressure does drop due to demand, then with Vaillants you will get a rapidly oscillating whoomph from the burner. From the other questions you have asked I don't think any responsible competent person should tell you how to sort your low pressure other than for you to call a CORGI engineer.
Yes, RGI should not give out advice on how to check appliances to anybody, 😡
and the only advice should be contact a CORGI installer, all gas applainces installed have to be notified to LBC, my advice to any body posting threads regarding any gas appilance would be
"If in doubt get a CORGI to CHECK IT OUT"😱...its for your own safety!!
Nominal – 3.24
+5% - 3.40
-10% - 2.91
You are TOLD the gas pressure at the meter is OK? Haven't you measured it? Are you GAS SAFE registered mate?
If there is more than a 1mb drop across that system it is AT RISK so the working pressure is important. Pipe size is important or there could be Sulphidisation
as roryd says get a gas-safe reg engineer out,safety first ,also you invalidate grtee,
house insurance,thats why we spend 5yrs doing an apprenticeship,and if like me you work for yourself 1000's in acs fees and gassafe registration,so no one is going to give you tech advise,nor should anyone else.your out of your diy depth
And a DOH! from me. I meant well anyway