Hi there again, I have an issue with mentioned boiler. Actually fan doesn't work. The displayed fault code is F02 what according to the service manual says that is "Air flow, Fan, Air Pressure Switch".
I have checked the vent, it's clear and shouldn't cause a problems, therefore I've checked out the APS, seems to be alright.
Tho the fan doesn't spin I forced APS to start ignition and that's fine, the rest works but the fan still doesn't spin.
Thus I checked the direct current (DC) values on the fan's supply cable and there's nothing, sometimes just low voltage but for no longer than 0.5 second.
All symptoms tells me that the PCB is faulty. Of course I've checked all the wiring and also tried to connect fan to 9V battery (it caused some movement, but the DC from the battery is to low for this fan IMO).
The part is quite expensive so I'd like to confirm my opinion with you fellas before I buy it. Thank's in advance.