I have a clients oil Grant boiler I fitted last year. It is a Vortex pro 26-46 system.
It is just a small system loop as it is a pool boiler. Heated through a heat exchanger directly behind the boiler.
I went to service today and took about a handful of rust off the baffles. There was even signs of rust on 2 of the chamber door nuts.
Boiler has a 150mm vertical flue about 2.6mtrs located in a pool pump house with all pool chemicals.!.. First thought on the rusty nuts was the pool chemicals in the air. But this does not explain the rusting baffles. Could this be result of a blocked condensate or flue fault.
I then done a combustion test and all spot on .
Any advice and ideas where to check appreciated .