View the thread, titled "Gravity DHW pumped CH radiator problem." which is posted in UK Plumbers Forums on UK Plumbers Forums.
Hi Guys, called to property with oil fired pressure jet boiler. loads of people looked at it in the past apparently but not sorted it. V old one pipe system with 10 rads, some old some new. Most recent somebody renewed the circ pump which is on the CH return to boiler about 1m away. The gravity DHW side (28mm) is absolutely fine. Problem appears to be that 2 rads never get hot (1 up and 1 downstairs), and then sporadically others do not get hot then on other days do get hot. Others mainly upstairs require to be bled regularly.
Our response was to drain system, clean F&E, renew all rad valves with lockshield & TRV sets, chemically powerflush via circ pump connections.
End result not much improvement! Did notice that after bleeding all rads that the rads only really bled properly with the system off. If we tried to bleed with the system running (to push air through quicker) then there was no air escaping or water to the rads?? as soon as pump was switched off air came hissing out. Quite confusing this one.
My next step is to recommend ripping old out and fitting new fully pumped but would welcome anyone's experience on this.
Jim
it doesent mater if they fit on either flow or return, if room gets hot and trv closes off automaticaly this will stop the circulation in the central heating!!! then tey will have no heating at all will they??
they need to be suitsble for one pipe, as blod has said. they have a larger bore " normal ones are to restrictive
it will still circulate, its a continuous pipe, tho rads will be cold
what if its a one pipe system that just enters the rad and then out the next end into the next radiator , the type where you cant turn the radiators off? the the water would have cooled down alot by the time it reached the 9tha nd 10th rad wouldt it????
Only shuts off the rad. Other rads have the flow going past them, not through them. One pipe is same as two pipe usually except the colder water continues to next rad in circuit.
Jim
Got to watch when bleeding a system with the pump on. Sometimes the vent is drawing air in! Try putting drop of water on end of your finger & pressing against air vent & water will suck in.
Already aware that the one pipe is standard one pipe, ie is in a continuous circuit with tails to rads. I'm thinking that continuous requirement to bleed is due to negative pressure somewhere. two rads not getting hot maybe down to blockage somewhere?
Hi Best, we did check that but all seemed ok, that's why I started head scratching as it's not every day we come across these old systems
with pump on return, circuit is always under negative pressure and pulls air in which will cause corrosion. mebe flush these two rads, one pipe needs good balancing imo
Your powerflush did very little if anything to the rads. It would have just pumped around the circuit.
The rads on one pipes work by gravity circulation.
The system is under negative pressure so trying to bleed the rads with the pump on isn't going to work.
Check the pipe runs to the rads that don't work especially if they are additions to the original system and fit the correct valves.
If the two rads that don't work well have long run of pipes from the main pipe, then they won't work well, if at all, I would think.
Better it's all ripped out! I have rarely seen these systems, but did come across a one pipe job a few weeks ago, that some idiot plumbers had taken long legs off the original rad pipes & obviously it didn't work as they had plugged it.
It's worth checking the pump speed. If it's too fast the rads won't heat up properly because there isn't time for the hot water to gravity circulate into the radiators.
Reply to the thread, titled "Gravity DHW pumped CH radiator problem." which is posted in UK Plumbers Forums on Plumbers Forums.