C
colled
I'm hoping someone here will know what the problem is. My setup is a Megaflow system heated by an Ideal classic boiler with 2 port valve to the heating circuit and another 2 port valve to the hot water cylinder (indirect). I've noticed that even with the hot water and heating switched off at the main controller/programmer the hot water is still being heated up to the same temp as normal, which is very hot but not enough to trigger the T&P valve. The heating remains off as expected. The boiler is firing up about every 10 mins or so for about 30 seconds all day and night so is getting demand from somewhere, I assume from the hot water circuit as that's what is still being heated despite being selected as off. I'm thinking the 2 port valve to the hot water is stuck on/open, but I've checked this and the manual lever is in the off (and is sprung open) position and doesn't seem to ever go into the on position even when the boiler is fired. Also I assume the boiler gets it's demand signal from this valve so if on all the time the boiler would fire all the time? or could it be the valve is opened and demanding all the time but the boiler is using it's own inbuilt thermostat to switch on and off? But then with the hot water switched off at the controller, why would a demand signal be sent to the boiler anyway? I assume demand is sent electricallly rather than just water flow? Anyway, does anyone have any suggestion as to why it's doing this?
many thanks for any help given!!
many thanks for any help given!!