These boilers have a thermistor probe in the plate heat exchanger, not a hot water flow switch
this keeps the water in the plate heat exchanger hot all the time ready for use, when hot enough the motor on the diverter valve is activated and boiler goes to heating water mode
This is way the dripping tap keeps boiler on hot water mode with no heating as hot water in boiler will never get hot enough to change to heating as looseing temp through tap, same as the old potterton puma which had wax capsule
So the problem is some were in the link when the boiler acts like above it will be the probe, motor on top of the valve or valve its self sticking as has to spring back up and this sticks also
This is why fitters do not like boiler, it as has the same common faults due to various possible parts going wrong, usually its one common fault caused by one part
Simple checks, if you remove the motor head and turn boiler off then on you will see motor move, if not possible motor, once motor head off diverter valve body the pin at the front should move freely, if not remove front on valve and lubricate pin, this only usually causes heating to come on with hot water
If motor ok and valve head then probable cause probe in plate heat exchanger located under boiler at rear
Can be tested with multi meter
Ref the power cut ,Ideal are thinking maybe external controls need resetting or may have been damaged if there was a power surge,you will have to make sure power to heating side of boiler