Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

View the thread, titled "LGSC how would you categorise this" which is posted in UK Plumbers Forums on UK Plumbers Forums.

Status
Not open for further replies.

SPC

Plumbers Arms member
Plumber
Gas Engineer
6 year old Vaillant ecotec pro with vertical flue in a close to inaccessible loft space, full length of flue is about 2.5m with one Of The fittings inside the inaccessible loft space, perfectly viewable from an access hatch. The flue has all of the screws in where it is supposed to, nicely patched in at the ceiling below, good lead slate above but there is no support bracket in the loft space where there should be, however the flue is not loose.

Checked the flue integrity which was perfect so I deemed this not an AR situation.

What would you have done?
 
AR it is then, Vaillant stipulate clips on every flue section. To hell with common sense.
 
I rang gas safe to get their opinion on it and the answer definitely sent mixed messages. The guy said I have to do a risk assessment of the situation and things like "you know what the answer is" but in his opinion if he was met with this situation he would not be shutting the boiler off.

MINDFIELD!
 
If it was rigid enough, sound and no sign of at having moved over the past 6 years, I would have probably given a warning advise notice !
I definitely would not turn it off.
 
If it was rigid enough, sound and no sign of at having moved over the past 6 years, I would have probably given a warning advise notice !
I definitely would not turn it off.
 
Status
Not open for further replies.

Official Sponsors of Plumbers Talk

Reply to the thread, titled "LGSC how would you categorise this" which is posted in UK Plumbers Forums on Plumbers Forums.

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Weekly or Monthly Email Digest

Back
Top