Has anyone installed a LLH on an open vented system? If so, have there been any issues or anything to look out for?
 
I've only installed LLHs on sealed systems to date.

I am quoting for a job where I'll be putting in 2 boilers (probably Viessmann) to provide 65-70kw total. It's an old system, old pipe work, old rads etc so would be too risky to convert to sealed...
 
I've only installed LLHs on sealed systems to date.

I am quoting for a job where I'll be putting in 2 boilers (probably Viessmann) to provide 65-70kw total. It's an old system, old pipe work, old rads etc so would be too risky to convert to sealed...
Boilers may need to be sealed but you could do a hybrid using a large plate heat exchangers so new boilers on sealed side & separate from the dirty old open vented side. I have not done one myself but understand it is being used as easer to clean / replace exchanger than risk a new set of boiler heat ex's.
 
How does that work chris? Like the idea of that but always thought that the circuit draws from header or am i in thick mode and not thinking ??
 
How does that work chris? Like the idea of that but always thought that the circuit draws from header or am i in thick mode and not thinking ??

Boiler to header is the primary circuit and then on the other side of the header the secondary circuit is to the plate HEX back-to-back with the CH circuit. This provides total separation and removes the need for sealing the CH, whilst the boiler/header circuit is sealed. I haven't done this yet, but have heard it talked about...

Do you know if there is some other type of HEX that can be used (other than a plate HEX) with bigger waterways that are less likely to clog up with gunk on the CH side?
 
Boilers may need to be sealed but you could do a hybrid using a large plate heat exchangers so new boilers on sealed side & separate from the dirty old open vented side.
If you did that, would you still need a low loss header? I wouldn't have thought so.

It would depend on what circuits there are on the system but the plate would be high resistance, so I would have thought it may be better to have a pump to deal with just this & then a header to distribute out to each circuit in the normal way.
The LLH will also act as a dirt separator (if installed vertically) being a low velocity area, that along with a strainer / magna clean type filter might help to keep the heat EX clear?
 
Last edited:

Official Sponsors of Plumbers Talk

Reply to the thread, titled "low loss header / open vented" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
Fishpond,
Last reply from
chris watkins,
Replies
13
Views
8,214
Back
Top