Natural Gas - calculating pressure drop

View the thread, titled "Natural Gas - calculating pressure drop" which is posted in Gas Engineers Forum on UK Plumbers Forums.

C

cardigan

The pipe from my gas meter to my Worcester combi boiler is 22mm. It is 16m long and has 6 right angle bends after the meter.

Does anyone know the formula for calculating pressure fall from coming into themeter at 21mb to arriving at the boiler?
 
I thought I was adequately sized but like they say 'size isn't everything.' I have a Worcester35CDi currently running off the end of my 22mm NG pipe. I was playing with the idea of replacing it with a Worcester38CDi but the British Gas salesman says it will not run off my 22mm pipe. Having formed the view that this should be an easy calculation and that someone somewhere must have produced a formula and that every CH engineer must be in possession of and using this formula everyday I am now wondering whether the formula in common use is the one where we suck our finger and hold it aloft to the wind.
 
Last edited by a moderator:
From the figures you have given with the boiler on maximum rate at 4.12m3/h. The pipe run of this length will only deliver approximatley 3m3/h. So it looks undersize in its current state.
 
The manufacturer specifies a degree of pressure not volume. Worcester state that the bolier needs NG delivered at a minimum of 16.5mb. The calculation must involve pressure arriving at the meter (MP) minus loss of pressure caused by friction in the pipe (L) The question is - how do you calculate the loss of preesure from the meter to the boiler?
 
Reg Man has just worked it out for you, in terms of gas rate. This shows that BG are right and the pipework would be undersized and would need to be upgraded for the 38CDi to be fitted.
 
Thanks and thanks for the link to the copper pipework doc there should be enogh infor inthere for me to saiisfy my desire for a formula
 
You could post here, see if there is anyone local to quote against British Gas
[DLMURL="http://www.ukplumbersforums.co.uk/im-looking-plumber-gas-engineer/"]I'm looking for a Plumber or Gas Engineer[/DLMURL]
 
The manufacturer specifies a degree of pressure not volume. Worcester state that the bolier needs NG delivered at a minimum of 16.5mb. The calculation must involve pressure arriving at the meter (MP) minus loss of pressure caused by friction in the pipe (L) The question is - how do you calculate the loss of preesure from the meter to the boiler?

21mbar working pressure at the meter then should have 20mbar on the inlet to the boiler. BS6891
 
Hi

Can anyone tell me the flow rate in cubic meters per hour of natural gas from the meter in an oridinary residential domestic dwelling house

TIA
 
Watching.

That's nice to know
icon5.png
 
Because I've found a formula to calculate drop in gas pressure and the formula requires the flow rate
Trick will be to find out how much gas each appliances will be using running flat out (kW input), then convert to amount of gas required to meet this. (clue = look at your gas bill for how much you get out of one one cubic Metre)
 
Last edited:
21mbar working pressure at the meter then should have 20mbar on the inlet to the boiler. BS6891
On these figures 18.5 Mbar at gas valve inlet as you are allowed 1.5 Mbar, across the internal gas Pipe and isolation valve on WB boilers!
 
To better ensure that two people taking a shower at the same time (in separate showers!) both get emough hot water

This will never happen with any standard combi, 38kw or otherwise.

And you shouldn't be concerning yourself with gas rates, pressures and formulas relating to such things
 
Last edited by a moderator:
On these figures 18.5 Mbar at gas valve inlet as you are allowed 1.5 Mbar, across the internal gas Pipe and isolation valve on WB boilers!

Yes Vern thats what WB say. Thats why I said on the inlet and not at the boiler inlet test point. I put an inlet test point just before the boiler isolation valve when I feel necessary on marginal jobs, it certainly prooves the pressure drop through the boiler valves and pipework.
 
Yes Vern thats what WB say. Thats why I said on the inlet and not at the boiler inlet test point. I put an inlet test point just before the boiler isolation valve when I feel necessary on marginal jobs, it certainly prooves the pressure drop through the boiler valves and pipework.

Yep good practice regards the test point just below appliance, had a 2 Mbar drop, from this point to gas valve inlet on an 837 combi, but some of this is the fan suction having an effect too, hence the tolerance.
 
What you really need is a "man's formula" not these ready-reconer's you will be requiring Pole Formula.
Please see attachedView attachment 10554

Dr Poles formula can be found on page 10 of this doc and you will see that the root factor covers both the numerator and the denominator . [DLMURL]http://www.mech.hku.hk/bse/MEBS6000/mebs6000_1011_04_steam.pdf[/DLMURL].

And, transornation of the formula for H gives h = ( s * l * q^2 ) / ( 0.0071^2 * d^5) i.e. D to the power of 5 not D times 5
 
Last edited by a moderator:
shouldn't be concerning yourself with gas rates, pressures and formulas relating to such things

I shouldn't but you should. I expect a 'professional' to come to my house and show me a mathematical equation proving that I need to pay to put in wider pipe. I expect that someone who is charging £50-70 an hour can do that. Is that asking too much?
 
I shouldn't but you should. I expect a 'professional' to come to my house and show me a mathematical equation proving that I need to pay to put in wider pipe. I expect that someone who is charging £50-70 an hour can do that. Is that asking too much?

What happened to trusting someone who clearly knows what they are talking about. If you have a problem with your car do you go down to the mechanic and make him prove his diagnostic skills in order to satisfy you that he isn't taking you for a ride? I know if I had someone ask me for a mathematical equation to prove that the gas supply needed upgrading I would tell them to stick the job up there arse. Anyone that even entertains having you as a customer is clearly a much more patient, understanding man than me. Either that or they are desperate for work.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Natural Gas - calculating pressure drop" which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
cardigan,
Last reply from
dancinplumba,
Replies
37
Views
10,960
Back
Top