Renewing 17yr old Gloworm combi boiler, running dom h/w and 15 rads, 40% are doubles. Water flow from stop valve has been measured as 6L p/m, is that enough to run system effectively?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Sinks are ok, shower is intermitent, runs cold then hot, bath is the same.Heating will run fine, hot water ideally requires at least 10L/m. How does your current boiler provide HW?