dmart7
I have an old Apollo 60B which is running well but has an intermittent boiling issue. It seems to be connected to the pump overrun stat but it works correctly most of thetime and I would be grateful for advice. Intermittently – once every few days - water boils in theboiler for a few seconds (banging and swooshing). This only occurs on the “LO” boiler stat andwith central heating running.It does notoccur on “HI” boiler stat nor if heating water only.The boiling and banging occurs only immediatelyas the boiler relights after cycling off via the “LO” thermostat, and only if,by chance, the pump overrun stat has just switched off the pump.
Normally,once the boiler has been on for more than half-an-hour (say), on “LO”, itbegins to settle down to a cyclic process:
If the boiling and banging occurs, it comes after about 80 minutes from cold start and happens when the boiler relights (4) a split second after the pump goes off (2) above. It seems that on one chancecycle, the overrun stat switches off the pump just as the boiler relights and the pump doesn’t restart (3).As the pump isn’t on, the water boils immediately, it bangs loudly for a few seconds and the burners are switched off by the thermostat.
Iam inclined to think the overrun stat is faulty but am not sure exactly howthey work and whether the way this one switches off and on, or notoccasionally, is at fault.
Normally,once the boiler has been on for more than half-an-hour (say), on “LO”, itbegins to settle down to a cyclic process:
- Theboiler heats for 10-15 mins, then the LO stat trips off the gas
- Thepump runs on for a minute or two (overrun stat), then it goes off
- After3-10 seconds, the pump turns on again
- Afteranother minute or less, the boiler relights
If the boiling and banging occurs, it comes after about 80 minutes from cold start and happens when the boiler relights (4) a split second after the pump goes off (2) above. It seems that on one chancecycle, the overrun stat switches off the pump just as the boiler relights and the pump doesn’t restart (3).As the pump isn’t on, the water boils immediately, it bangs loudly for a few seconds and the burners are switched off by the thermostat.
Iam inclined to think the overrun stat is faulty but am not sure exactly howthey work and whether the way this one switches off and on, or notoccasionally, is at fault.