Hi, I'm new to the forum, and hope someone can help.
We have an ageing (30 year old) Ideal boiler in a house we recently bought and would like to replace it with a 2004 Potterton Paramount 80 from a swimming pool we are taking out of service. The Paramount is in good nick and hasn't been used very much.
The old Ideal has an output of 115,000 BTU/hr which is about 33kW. The Potterton is max 80 kW but modulates down to 20 kW min.
The 6 bed house has a max heat requirement of about 37 kW according to my whole-house calculations and those of a recent installer who went round.
It's a vented system with a hot water cylinder.
The installer says the boiler is too big, and Potterton tech seem to agree. I really don't want to chuck it out, and need to know why. Firstly the boiler can be set to max out at 40 kW in software, but I agree the min output is still 20 kW. However the existing one is blasting away at 33 kW all the time, so...
Any advice gratefully received.
We have an ageing (30 year old) Ideal boiler in a house we recently bought and would like to replace it with a 2004 Potterton Paramount 80 from a swimming pool we are taking out of service. The Paramount is in good nick and hasn't been used very much.
The old Ideal has an output of 115,000 BTU/hr which is about 33kW. The Potterton is max 80 kW but modulates down to 20 kW min.
The 6 bed house has a max heat requirement of about 37 kW according to my whole-house calculations and those of a recent installer who went round.
It's a vented system with a hot water cylinder.
The installer says the boiler is too big, and Potterton tech seem to agree. I really don't want to chuck it out, and need to know why. Firstly the boiler can be set to max out at 40 kW in software, but I agree the min output is still 20 kW. However the existing one is blasting away at 33 kW all the time, so...
Any advice gratefully received.