Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

View the thread, titled "performa 24 no hot water" which is posted in Bathroom Advice on UK Plumbers Forums.

S

scoullar

have another problem with a pott performa 24 tap running boiler ignite for about 30 secs and cuts out and ignites again after about 2 mins havnt done any checks yet going tomorrow im thinking diverter or hw sensor or hw plate which is most likely in your experience
 
you need to test all 3 its very common to just be a pinholed diaphragm,if the flow is getting very hot suspect the plate heat or diverter thermister wont be in question the 24kw only has a primary ntc so if heatings working rule that out
 
flame failure lockout was due to pcb that probs solved changed diverter and hot water section water is coming out luke warm intermittently and left hand heating pipe is getting hot could the new diverter be faulty never had new one faulty before
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "performa 24 no hot water" which is posted in Bathroom Advice on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Weekly or Monthly Email Digest

Back
Top