Came across a prima today, while doing a job next door. Flue terminal was facing the property i was working on.
the centre of the terminal was missing , so I had a quick look inside. Big hole on the inner flue. Had a word with the owner, she said it had been serviced by a large national company 2 months ago!

found a replacement online. Do these swap easy ?
[DLMURL]http://www.gas-spares.co.uk/CATALOGUE/POTTERTON-MYSON-SPARES/BOILERS-STDSYSTEM/PRIMAPROFILE-Range/POTTERTON-PRIMA-basic-range/PRIMA-50F/FLUE-REMEDIAL-KIT-terminal-Cw-inner-flue-pipe[/DLMURL]
 

Attachments

  • image.jpg
Last edited by a moderator:
Came across a prima today, while doing a job next door. Flue terminal was facing the property i was working on.
the centre of the terminal was missing , so I had a quick look inside. Big hole on the inner flue. Had a word with the owner, she said it had been serviced by a large national company 2 months ago!

found a replacement online. Do these swap easy ?
[DLMURL="http://www.gas-spares.co.uk/CATALOGUE/POTTERTON-MYSON-SPARES/BOILERS-STDSYSTEM/PRIMAPROFILE-Range/POTTERTON-PRIMA-basic-range/PRIMA-50F/FLUE-REMEDIAL-KIT-terminal-Cw-inner-flue-pipe"]FLUE REMEDIAL KIT terminal C/w inner flue pipe - Gas Appliance Spares (Preston) Ltd[/DLMURL]

remove old terminal that new one slides over so quite east to do,its called a remedial kit
 
Last edited by a moderator:
There is 2 different sizes of remedial flue. Have one of each in van. These flues are like tinfoil.
You just cut the remedial flue to size si it overlaps the corroded inner by few inches.
 
There is 2 different sizes of remedial flue. Have one of each in van. These flues are like tinfoil.
You just cut the remedial flue to size si it overlaps the corroded inner by few inches.
i bet I've ordered the wrong one!
 
They are easy to fit as long as the flue is out far enough so that the cement don't cover the screws you need to undo to get the terminal off!! then its a bit of a pig.
 
They are easy to fit as long as the flue is out far enough so that the cement don't cover the screws you need to undo to get the terminal off!! then its a bit of a pig.
More often than not these are the ones that need changed.
You chisel away rock hard cement to expose the screw heads which are all rusted and damaged. A 20 min job taking an hour. :annoyed:
 
They are easy to fit as long as the flue is out far enough so that the cement don't cover the screws you need to undo to get the terminal off!! then its a bit of a pig.

impact driver or/and a quality hss bit,screws not normally hard to drill
 