I would like to know if there would be any issue on changing the water supply from tank fed to mains supply for the Prima profile 30e boiler. The boiler feeds a hot water storage vessel before distrubution to taps
 
I would like to know if there would be any issue on changing the water supply from tank fed to mains supply for the Prima profile 30e boiler. The boiler feeds a hot water storage vessel before distrubution to taps

No problem what so ever,boiler has high limit thermostat fitted,just remove header tank and fit filling loop,pressure release valve,pressure gauge and correct size expansion vessel for system,will not be that big with boiler only 30.000 btu,pressurise system to around 1/2 bar only and away you go 🙂
 