I would like to know if i can run the prv pipework up and then out of the building, thanks.
I would like to know if i can run the prv pipework up and then out of the building, thanks.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
You can't, but I don't see why not to be honest. I've seen warm front jobs with the PRV terminated into an F&E tank..
thats putting in a remote one tho, think op means running prv pipework upwards ?Is that like the baxi high level PRV , 2.5 bar and tee the existing one into the return?
really??
thats putting in a remote one tho, think op means running prv pipework upwards ?
oops 🙂Was reffering to mikegas's comment, not heard of any other kit that means you can take PRV up hill?
Really - I don't see why not? No 3 bar's not going to have much problem going up hill!
or
Really - Yes, I have really seen PRV's fitted by warmfront terminated into F&E's sited underneath the boiler in an airing cupboard in the middle of a house. The stupid thing was they had lifted the floors and drilled through the outside wall to bring a 22mm gas in so no idea why they didn't run in the PRV at the same time. I've seen 3 like it. (used to do warmfront work and these were ones we got sent to remedy.)
You can't run uphill with a prv because of freezing
Scenario
Boiler on 7 day programmer.
Boiler comes on. F and r frozen. Expansion vessel broken
Prv goes up hill and because of failed EV the prv is blocked.
Temp shoots up. Pressure goes mental.
That's why a prv should always fall
Another point to watch is linking a prv overflow to plastic. if you consider the likely temperature of the discharge water could be steam like temperatures, then what would that do to plastic?