After some ideas, I've got a house which is installed with a system boiler, when the hot water is turned on using the programmer the radiators also get warm, checking the pipework underneath the boiler, both the how water flow and central heating return are red hot! Any ideas how to rectify?

Cheers
 
As you said you have system boiler that means you must have main or balanced cold feed into your sealed cylinder. In that case the problem lies on 3 port valve or the programmer. Check your 3 port valve, unless if it's stuck on manual open position. If it's stuck on fully manually open position then you get both hot (radiator and water) at the same time.
 
Piped wrong and there is a loop through rads return caused by one or more rad tee offs on return, with one of those between return to cylinder and boiler.
 