its an electric shower, used everyday, so doubt it stagnant water, any ideas?
 
the wiring in the pull cord switch thingy has charred. the wire from the circuit breaker to the switch. charred back about 1 inch. ive not checked yet if it was because of a lose connection. would it be ok to cut back the wire past the charring, and reconnect it to the switch/new switch, or does the whole wire need replacing?

thanks again.
 
8.5kw
6mm? not sure how to measure this, but its bigger than socket t/e but not huge
40 breaker

If you can see enough of the cable, the size will be moulded into the sheathing.

The cable is likely inadequate. 6mm can carry up to 47A if clipped to an open wall. As soon as you run it through trunking or within a stud wall the load capacity drops. Even more so if the cavity is insulated - to as little as 34A. Your shower will draw almost 39A.

I would strongly advise getting a sparky in to assess the cable run and would certainly look to uprating it to 10mm2.
 
Cable definitely undersized, typically shower has been replaced with a more powerful one
Rules of thumb 8.5kw -= 36A so need 40A MCB and min 10mm2 cable and new 40A double pole pull cord switch located in the correct place - there are regulations might need RCD/RCBO
- You need to get a qualified sparks in to check above and run new cable from CU
 