recently got called out to a myson floor standing natural draught boiler.
Very simple boilers so you would think them not to be much of a problem when it comes to troubleshooting. When i first arrive the burner would not light, despite there being a nice steady pilot. So i test everything down to the gas valve and all was fine, thermostat functioned, thermocouple workes fine holding open the pilot and i was getting 230v to the gas valve.
So i replaced the gas valve thinking sorted... but no. Still no burner ignition despite there being 230 at the valve, and even the burner pressure getting upto 19.5mbar as specified. So i cleaned the burner and the injector, still no flame. What am i missing?
im starting to think it could be down to a blockage in gas pipe, i suppose i could test for this by letting the gas valve open and doing a gas rate. Surely cant be it though
Very simple boilers so you would think them not to be much of a problem when it comes to troubleshooting. When i first arrive the burner would not light, despite there being a nice steady pilot. So i test everything down to the gas valve and all was fine, thermostat functioned, thermocouple workes fine holding open the pilot and i was getting 230v to the gas valve.