only getting 31mb (LPG dungs valve) at inlet pressure when boiler is on at max. drops to 29mb when cooker is switched on , they are the only 2 appliances in the house. aprox 7 meters from regulator to boiler , all piped in 15mm with 7 or 8 elbows . why somebody would pipe it up in 15mm is beyond me. some idiot buit a wooden boxing next to the boiler so it had no side clearance , should have 5mm. flue pops up thru the roof clipped on to next doors gable end , so not getting its 500mm clearance from obstruction (was a bungalow in the middle of a row of houses stuck to each other). prv run in overflow pipework . around 1m of the flue was boxed in. asked customer to move some stuff out of the way so I could access it to have a look at flue inside "why do you want to do that? previous plumber did not open it on the last 3 cp12s he did" . Neither did he pick up any faults on the installation! so guys if I renew the pipework to 22mm do you think it will be ok? I AR the boiler as it was undergassed by so much, would you have done the same?