View the thread, titled "Unvented cylinder size" which is posted in UK Plumbers Forums on UK Plumbers Forums.
TFGplumbing
Hiya guys
I currently specing a job for a 5 bedroom house with x5 ensuites. Could anyone advise me on sizing cals for unvented cylinders.
Thank you
Hiya Shaun
6.5 standing
6 dynamic
22litre per min plus - it over flowed my guage
25mm mdpe main
x1 bath x 4 mixers
ta last q how many outlets are they planning on using at once /demand like 4 showers each morning etc
400l or 300l fast reheat
4 showers lets say 12lpm
60/40 split
8 hot / 4 cold
average shower 10 mins
so total per shower 80l hot / 40l cold
over 4 showers 320l hot / 160l cold
if you allow this for cylinder temp will give you a bit of wiggle room as people dont have 60dc showers 😀
i would allow a good 25kw for a high recovery
10kw for re heat within 90 mins is you can add more if the coil will take it eg 20 kw for 45 mins etc
Okay so I've got a Heat loss of about 24 kw for the rads including a 15% margin for pipework etc etc
The system will be run from a oil boiler, initally I have thought a 32kw would be suitable. The coil on the propsed 300 litre cylinder is 39kw.
Whats your opinion on fitting a larger boiler?
depends stagger the hot water times then you can go with a 28kw
if they want them both on the same time around the 40 kw mark
How about putting in a flow switch & timer device so that after so many mins of HW flow, the boiler automatically initiates HW reheat? That could operate in parallel with the std HW schedule.
you could do how water priority ish
with regard locating this beast of a cylinder, 300kg odd is alot of weight do you guys do load cals for placing units like this on joists
normally try and get it close to a load bearing wall or add extra support in
As Shaun says, get close to a wall first. Personally, I've always put mine on 25mm ply spanning joists and screwed through into them to distribute weight as much as possible. 300KG isn't that bad. Tis only three rugby players in a huddle 😉
w plan system
Hot water priority, if there is a demand for hot water & heating, the hot water is heated first
Ahh. Sorry, bit of a thick day!
My point was to try to add a bit more monitoring of HW use rather than rely on fixed stat hysterisis alone. Ideally, one would replace the stat with a sensor so the two can be used in parallel. It would however require a microprocessor & programming to deliver...
Reply to the thread, titled "Unvented cylinder size" which is posted in UK Plumbers Forums on Plumbers Forums.