View the thread, titled "Vaillant ecotec pro 28 f28" which is posted in UK Plumbers Forums on UK Plumbers Forums.
Hobo128
Been out to this boiler tonight. Open hot or ch demand boiler fires up for about 2 - 3 seconds and then goes off, repeats its self about 4 more times the locks out with f28.
Ive checked the gas valve for resistance.
Checked continuity of gas valve leads.
Check earth to boiler.
Took out spark electrode which is sparking and checked inside burner which is squeeky clean, also condense is not blocked. Fan runs and pump runs.
Any ideas
It doesnt make any noises when alight. Inlet pressure 20mb.
Is there a way to check flame rectification?
sounds like its not sensing a flame i would say probes
give them a clean with some sandpaper
Could be. But I would also check the working at the valve. Had a faulty regulator before Christmas and when the boiler was on full power was only giving about 6mbar.
Ok
Inlet working at meter 21mb. Inlet working at boiler 20mb. Probes are clean and have been cleaned again with wire wool by my self, I have removed them and are sparking. I've check resistance of gas valve which seems fine and have check earth from probe to boiler casing and boiler casing to pcb and so on. Condense is clear and all harness wires from visual inspection seem fine. I feel like it maybe pcb that is at fault. Any takers? Also , when boiler fires very very briefly burner pressure is -8mb
Ok
Where are you reading that -8 from?
Have you checked the polarity?