Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

View the thread, titled "Valliant EcoTech High Pressure" which is posted in UK Plumbers Forums on UK Plumbers Forums.

Hello. I am a homeowner and have a Valliant EcoTech 835 (2017). Serviced every year and worked like a treat until about a few months ago when I notified the pressure reading was too high (> 3 bar). My plumber came and did a regular service and told me the boiler is in tip top condition. The pressure remained high upon inspection. To relieve, I use the radiator valve to remove some water. I am then told that I need to replace the expansion vessel and PRV. Both done. Pressure was ok for about a week then started climbing and now is again consistently >3 bar. My plumber now tells me I need to replace the Pressure Gauge Sensor. Just wanted some advice from the experienced heads here. Am I going down the right path or should I be looking at a different solution? Thanks
 
1 is filling loop passing.
2 if it’s a combi could be a breach between the plates on plate heat exchanger.
3 Vaillant pressure sensors tend to get clogged up so either stick on a reading.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Valliant EcoTech High Pressure" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Weekly or Monthly Email Digest

Back
Top