Vertical radiator problem

View the thread, titled "Vertical radiator problem" which is posted in DIY Plumbing Advice on UK Plumbers Forums.

I have a vertical radiator with 5 sections. Four of the sections warm up ok but the fifth remains cold. The problem section is the end section on the left, the hot water flows in from the right. I have removed and flushed the radiator with no success. Any suggestions welcome.
 
has it ever worked if not have you fitted it the right way round some have a small dimple to let you know that that is the bottom of the rad,
It has never worked since I bought the house earlier this year. I will check for for a dimple or some indicator of the bottom when I return home on Monday.
 
Can you photograph the rad do you know the make also
Please see photos attached. Sorry I do not know the make. There are 2 tappings at the top of the rad, one used for the bleed valve; could these indicate the rad is upside down?
20201206_200558_resized.jpg
20201206_181134_resized.jpg
 
Removed the rad yesterday. The baffle was located at the top which I guess confirms it had been fitted upside down. I reconfigured the rad, adjusted the wall brackets and it's now working fine. Thanks for your help.
 