Hi, new to this forum.
Wondering if anyone can shed any light.
I have a Viessmann Vitodens 100-W WB1B 30kW Combi Boiler and it's been installed around 10 years so I know it's gradually on it's way out.
I have had no real issues apart from having to have a new pressure vessel fitted 3 years back.
Recently my boiler has started to increase pressure rapidly.
Sitting at 1.5 bar it now heads towards 3 bar within a matter of hours.
I release the pressure by draining water from a radiator.
I initially thought it was a filling loop problem so plumber has changed that and also fitted a new pressure vessel.
Next day pressure starts to increase again!
I have disconnected the filler loop to take that out of the equation and yet pressure still increases.
This is what I can't understand.
If it's a completely sealed system, how come when I turn the stop tap off the pressure remains the same?
Only other thing I could think of is the heat exchange pin-holing.
Asked my plumber and he said if its the heat exchanger than scrap it!
He didn't spot any water within the boiler, but again he wasn't looking for any so be interested to get someone else's opinion before I shell out for a new boiler?
If I need to, would you suggest sticking with Viessmann or jump ship and go down the Worcester route?
Many thanks.
Wondering if anyone can shed any light.
I have a Viessmann Vitodens 100-W WB1B 30kW Combi Boiler and it's been installed around 10 years so I know it's gradually on it's way out.
I have had no real issues apart from having to have a new pressure vessel fitted 3 years back.
Recently my boiler has started to increase pressure rapidly.
Sitting at 1.5 bar it now heads towards 3 bar within a matter of hours.
I release the pressure by draining water from a radiator.
I initially thought it was a filling loop problem so plumber has changed that and also fitted a new pressure vessel.
Next day pressure starts to increase again!
I have disconnected the filler loop to take that out of the equation and yet pressure still increases.
This is what I can't understand.
If it's a completely sealed system, how come when I turn the stop tap off the pressure remains the same?
Only other thing I could think of is the heat exchange pin-holing.
Asked my plumber and he said if its the heat exchanger than scrap it!
He didn't spot any water within the boiler, but again he wasn't looking for any so be interested to get someone else's opinion before I shell out for a new boiler?
If I need to, would you suggest sticking with Viessmann or jump ship and go down the Worcester route?
Many thanks.