Replaced heat exchanger, both HW and CH motorised valves and actuators, PRV, expansion vessel, high limit thermostat, both inlet and outlet service valves and circuit board.
No above floor leaks apparent.
Switched off electrical power to unit. With system cold, pressurised system to 1bar and closed both (brand new) service valves, pressure went down within 2 hours to 0.5bar. Removed boiler covers so heat exchanger visible to check for any signs of water. None apparent anywhere. No water dripping from PRV or any joints in the boiler. Where is the water going!
Attempted to let water in via loop with the service valves closed. No water allowed in. IE no flow heard. (Think this would show if (new) service valves were bypassing water?) Closed loop again.
When return service valve opened, pressure returned to 1bar but dropped soon after when closed again.
Doing this repeatedly the pressure eventually dropped to 0.25bar.
When new pressure vessel fitted (8L, original rated at 4.5L) and system refilled to 1bar, upon firing up the system, the pressure rose rapidly to 2.25bar and the PRV dripped. Brand new expansion vessel is holding (nitrogen) pressure so why did it not accomodate the increased pressure. The flexi hose was checked for blockages before fitting . PRV stopped dripping when the pressure fell to 2bar.
As long as the radiators, which all heat properly no cold spots, are operating. IE the timer is set to ON, the pressure remains fairly constant. It drops to almost zero when CH timer goes to OFF.
The usual tests which I have performed as per advise don't seem to give the expected results.
E.G.
Closing the service valves should show whether it is the boiler or pipework at fault.
Rapid rise in pressure points to expansion vessel.
I'm at a complete loss and very frustrated by all this. I feel the leak is under the floor but there is no access. I don't want to tear up carpets , laminate and flooring until I am sure.

Any ideas?
 
Two bottles of leak sealer. Would have been my starting point and then external expansion, boiler parts just cost more than the boilers worth , about 150 times it current value. Also fit a monument test gauge as some times it's the boilers own gauge that's way off and let's u think ur having the wrong problem.

Buy a monument test gauge. Cap flow and return and attach gauge to filling loop where it joins ch. bump it up to 3 bar, wait for 24hrs.
 
Last edited by a moderator:
No I'm not a gasman or a plumber. Just a poor sod with a broken boiler. I thank you for your informative help Ermintrude. Glad to give you a laugh H4S. I did not fit these parts. I paid a registered guy to fit them. I just did the tests I was advised to do by searching the net when the problem persisted. I realise the boiler is not the best by a long chalk. It started off with an obvious leak in a motorised valve which I had repaired then when that didn't fix the problem...... and so on.
 
Call your gsr back to do his job properly.

We cannot and will not give advice on the installation or repair of boilers, cookers or ANY gas appliances for your own safety.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Vokera 14e pressure drop odd symptoms" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
rytenuff,
Last reply from
Dotty,
Replies
7
Views
1,317
Back
Top