Had a call for boiler lighting with a bang( and what a bang it starts with!) , checked and cleaned spark electrodes and did a tightness test between isolating valve under boiler and gas valve, it dropped 1.2 mbar in 2 mins . I kept gas supply off for 1st ignition attempt then switched on for 2nd attempt no bang . Redone tightness test stayed solid this time . Is it possible solenoid on gas valve sticking open a little at times? Plugged gas line until get new valve to try
 
Sounds a reasonable explanation mate. Did it do it after your tinkering at all?
 
Nope started sweet as a nut then , but maybe because chamber was empty of gas . Have ordered a valve for call back to see
 