View the thread, titled "WB 28CDi" which is posted in UK Plumbers Forums on UK Plumbers Forums.
peteisfishing
Evening all,
of to look at one of theses tomorrow, customer has DHW no CH, any common WB faults that i should be looking for?
Cheers
its Probably fec----------------------- faulty external controls is the obvious thing check
I will check thermostat & programmer, is there anything less obvious that i should be looking for, trying to save a bit of time thats all, for instance divertor valve? Just after a few pointers please
thanks Quality
if this is the worcester with no plate heat exchanger look at pump also theres no divertor on that model not gospel as im **** at which worgester is which
The 28CDi has a diverter valve, but if the diaphragm fails then it normally only causes problem with hot water. As already said above, check external controls first.
Martin.
Evening all,
Cheers
go to the worcester bosch site, hit the installer section and look up discontinued products and pull up the 28 cdi, save the instructions pdf onto a laptop and take it to the job with you and it has a fault finding guide to follow
used same file to day to service and set up one that had never seen an engineer since it was installed, new fan, tighten up a link on the controls section that was loose and giving a similar problem to yours and removed what looked like a birds nest in the flue. custard informed me it had never given him a problem until the fan collapsed over the weekend!!!!!!!!!!!!😱
If you do a lot of services/repairs then invest in one of these from Ebay: 4500 INTERACTIVE BOILER MANUALS ON 10 CD-ROMS BY GASPRO, only 12 quid inc P&P worth every penny.
Martin.
Went to the job today, looked at the wiring, no external controls fitted then went to isolate the boiler at the spur and another wire was going in to it!!........asked the customer if she had any controls, answer " well, we used to havce a thermostat but it fell off so we just connected the wires together!".....low and behold there they were, two core hanging from the ceiling which had been wired up to the fuse spur to create a switch.........disconnected it and replaced the LS LR link and it worked fine.....they now want a RF stat/prog fitted and a flush.......
Thanks for all the help...
PS: CD's ordered:
Worcester did a RF stat (ACL Drayton) for the CDi range which the receiver fitted in place of the clock on the front of the boiler (Grey plastic control panel RH side) not sure if its still available and how much.
Martin
Reply to the thread, titled "WB 28CDi" which is posted in UK Plumbers Forums on Plumbers Forums.