View the thread, titled "well suction negative pressure" which is posted in DIY Plumbing Advice on UK Plumbers Forums.
buzzz49
My pump is lifting water about 20 to 25 ft through 1-1/4" pipe at about 800' above sea level. Can anyone calculate the negative pressure at the pump for me? I'm just not that bright. I've recently installed a check valve near the pump and am having some issues with the system sucking air in and losing prime. Just curious to know what numbers I'm up against.
How is the pump primed??, some pumps have a foot (non return) valve in the bottom of the pipe to keep it full of water when the pump stops, if its only loosing the prime when pumping then it may be pumping at too high a flow resulting in insufficient NPSH, see below, can you post a link to your pump.
All pumps require a NPSH (net positive suction head) of ~ 0.5M (or so), it will be in the pump manual.
The NPSH is the atmospheric pressure (absolute) - the suction lift - the suction pipe friction losses.
Normal atmospheric pressure (absolute) is 1013mb, at 800ft elevation it will be ~ 992mb, 9.92M, suction lift is 25ft, 7.6M, if your 1.25ins pipe is 1ins ID, then the friction loss through 25ft would be ~ 1M when pumping 50LPM, so the NPSH will be 9.92-7.6-1.0, 1.32M which should be adequate, (pump details will tell).
Theoretically the negative pressure will be the height from the pump suction to the well water level, say 25ft=7.6M=0.76bar,11.0PSI with no pumping, and 7.6+1.0, 8.6M,0.86bar,12.4PSI when/if pumping @ 50LPM.
Reply to the thread, titled "well suction negative pressure" which is posted in DIY Plumbing Advice on Electricians Forums.