B
Billy Bob Bob
went to a 2 year old performa 30 HE today,burner only lighting one bar,not cross lighting and locking out,no other gas appliances in the house so i crack the inlet test point,hear a hiss put my gauge on 22 mb,lights boiler it drops to zero,looks like governor issue,goes to meter,remove TP,no gas,remove meter plenty of gas,meters failed (1 year old meter:bowwow🙂 called wales and west utilities,esp turns out finds some weird grease inside the meter has gone into the gas supply???? anyway fits new meter,TT leaves me to commission GR the boiler comes back as 35 kw????? checks bp 16 mb not 12.2 mb cant get bp down lower than 8 ch,14 dhw removes modureg green gunk in gas valve looking like a new gas valve is going to be needed,now how many people on finding 22 at the inlet would after finding 240v at the gas valve gone and changed a expensive valve to find the faults still the same? dont ever forget the basics it will save you money,the outcome is still a faulty gas valve but try explaining to a custard that you faulted it right the first time