buckley plumb
its been one of those wks boilers seem to be getting the better of me . been to worcester 24cdi rsf today htg works ok but on hw it works for 30-60 sec then the red hw demand red light flashes quickly and the boiler has to be turned off to reset and it will then repeat the same.checked the connections on st 16 - the yellow and red wires should be 1-30 k ohms got 6.5 kohms on both colours / the violet and browns should be less than 100ohms they were 68ohms .checked the pump by trying to stall it with screwdriver that was ok / checked the plate to plate got a differential across it of 10 degrees so assume its ok / checked and set gas burner press high and low / called worcester and they said poss plate but i dont think so . tried a few times then it worked so turned tap off and on and was working left tap on for 20 mins and all was ok so definately rule out plate. just got a call saying its doing the same thing again. i dont want to throw parts at a boiler of this age anyone any ideas. could it be a thermistor fault