Hello I'm new on here so apologise if this has already been covered but couldn't find anything on the search.

I am looking for some advice on ballancing a single pipe central heating system. My question is should i be striving to achieve the 11 degC temperature drop accross each radiator, as you would do with a 2 pipe system pipe system, or should i just try to get them all as close to the same temperature as possible?

Also the upstairs loop is tee'd off the downstairs loop but has a gate valve on the return pipe before it feeds back into the downstairs loop. what would this be for? Is this something to do with the ballancing the upstairs loop?

Many thanks.
 
Yes, its for balancing the loops.

It's a right pain to balance a single pipe system. First you need to open up all the valves and lockshields, balance the loops, then start at the radiators at the end of the loops and work your way to the front.

Do it by feel - if you're trying to get set temperature drops you'll end up pulling your hair out!
 
Thanks for your reply WHPES,
When i'm ballancing the upstairs and downstairs loops where is the best place to "measure" the temperature.
logic suggests to me that it should be on the return pipes just before they join back up at the Tee, is that right?

As for the rest i'm basically trying to get all radiators on each loop as close to the same temperature as possible, not concentrating too hard on the actual drops!
 
Across flow and return.

Bear in mind you'll have to be constantly checking all of them as you go on. Single pipe systems are a nightmare!
 
Thanks, I know they're not the best but at least it will keep me off the streets until i get round to adding another pipe next summer!
 
Status
Not open for further replies.

Reply to Advice on balancing a single pipe system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
353
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
240
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
197
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
253
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock