13
Hi all,
Quick question. I have a baxi 105e instant that has a Diverter valve issue. The bypass is allowing hot water around the bypass pipe and into the CH return pipe. I have looked at a rebuild kit and it seems that there are 2 listed. One is a cartridge type and the other more a kit. My question
Is, can the cartridge replace the older style sliding spool or are they not interchangeable ?
Thanks
Roseyp
 

Attachments

  • 78AE5131-0B28-4C12-9364-DD9E54422F3D.jpeg
    78AE5131-0B28-4C12-9364-DD9E54422F3D.jpeg
    578.2 KB · Views: 22
  • 8EF9AFAB-2C7F-440B-83A0-4AFFD94EC7CA.jpeg
    8EF9AFAB-2C7F-440B-83A0-4AFFD94EC7CA.jpeg
    1.3 MB · Views: 20
One on the right is for an external bypass but you have to check the hot water plate isn’t blocked as this will have the same symptoms
 
One on the right is for an external bypass but you have to check the hot water plate isn’t blocked as this will have the same symptoms
Hot water flow rate is good, no change really just taking longer to warm up. Boiler deffo has the external bypass as I can feel the pipe getting hot as soon as the dhw fires up. Goes from the rear of the Diverter to the rear of the ch return manifold. I will drop the plate heat exchanger out as I have new seals, but it either rebuild the Diverter with the kit, or get a new Diverter valve. Trouble will be the part numbers seem the same for the valve whether it’s an external or internal bypass, so I need to ensure that I get the correct one
Thanks for help though
Roseyp
 
The right one is for the 105 the left one is for a duo tec etc
 
A refurb valve is only £35 so maybe go that route. This is only a stop gap as I’m looking to get the boiler replaced before Xmas
Thanks again
Roseyp
 

Attachments

  • 91D65200-6ACC-46BA-9480-53CB0DCA01E2.jpeg
    91D65200-6ACC-46BA-9480-53CB0DCA01E2.jpeg
    234.8 KB · Views: 14
Do you have to send the old one back ?
 

Reply to Baxi instant 105e Diverter valve repair in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi all. After some advice before I get some quotes. I have a 19 year old baxi 105e instant that needs replaced for something more efficient. I’m...
Replies
4
Views
2K
Hello all, I should start off by stating that I'm not in the industry - I'm just a DIYer with a "what-if" idea. Hybrid systems and solar...
Replies
6
Views
1K
    • Like
Hi all, We recently purchased a house and nothing seems to work correctly here, I've spent weeks rectifying issues. Plumbing, electrical...
Replies
47
Views
5K
My kitchen radiator is filling with hot water despite my TRV being set to 0. It's blazing at maximum. This goes for the rad when I try two...
Replies
6
Views
2K
I’ve recently moved into a bungalow with an open vented central heating system installed in 1987 with 8mm microbore running to the 10 radiators...
Replies
12
Views
5K
Back
Top