if its a 24kw boiler and you get that gas rating it and the fga checks out ok ? why then do you need to do burner pressure ?
 
so you are assuming that the person who fitted the boiler in the first place did so correctly? personally i would assume nothing.
 
I had one today Worcester 240 RSF. Screw for burner pressure wouldn't turn and as I have a habbit of snapping screws I was reluctant to force this one. No MI, I'm sure the boiler is a 24kw but the heat input is 30kw for DHW. Gas Rated this at 29kw, FGA 0.0007. Working pressure. Seals, flame picture and burner insulation all good. I had a cooker and a boiler it took me 1.5 hours is that normal for a landlord certificate 2 appliances. Or am I just slow?
 
its around 10mb for 24kw boilers aint it ?
Guessing/assuming is not good enough as far as I am concerned. Off top of my head a Worc. 24 CDI BP is 13mbar to name but one.

Ideally,(although rarely carried out) it is good practice to do BP & Gas Rate where possible. How do you know the correct injector is in place otherwise. It is possible to have an LPG nozzle not been swapped for a gas one or vise-versa. Doing a Gas Rate and BP would indicate this as the readings would not tally up.


As others mentioned, unless you know the appliance settings, in the absence of a data plate, MI's or info from manufacturer you should not be carrying out any work on the appliance. Simple as that.
 
1.5 hours for cooker and boiler , took me about hour and quarter to do each boiler service today not sure if thats slow but then i'm usually install. As far as i'm concerned working with gas isn't a race rather take my time and double check again if not sure .
 
Well if there is a gas meter with pipework leading from it to the boiler, I'm happy to assume its Natural gas. If the boiler case states "Joe Bloggs 24 cdi" for example, I will then ring the "joe Bloggs" tech line and confirm the appliance and ask for the burner pressures which I will then check and adjust accordingly. Simples.

ive seen lpg water heater connected to natural gas
 
Status
Not open for further replies.

Reply to burner pressures in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts...
Replies
3
Views
761
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not...
Replies
1
Views
633
Hi I moved into a property where the pressure is slightly low and they have this super duper shower but pressure is somewhat lacking. I have had...
Replies
0
Views
232
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
555
I need someone to replace my boiler, I am thinking to get an Intergas HRE 24 SB. Our current boiler (and old Ideal) is in the kitchen, and we...
Replies
0
Views
352

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock