Having done some Googling, I think my second diagram, showing the flow connected to the return, is essentially a bypass at the furthest end of the CH loft piping. From what I can gather this isn't required, or particularly good practice. Also, my ecoTEC 637 system boiler has a built in bypass valve.
So, assuming I connect up the loft radiators as shown in the first diagram, if ALL the loft radiators and towel rail are closed, the flow of hot water will simply "stop" in the loft, but will continue on the first and ground floor.
That is correct. As you have worked out, if you close all the rads on the loft part of the system, the water will stop flowing through the main flow and return but only in that section. The rest flows perfectly fine and normal. Linking the flow and return will introduce a bypass, again as you have realised and this may stop the rads in the loft from working at all as the flow will take the path of least resistance and probably fail to flow through the rad at all or at least very poorly.