I have a problem on a site where the flue on a HRM Wallster is too close to an extract vent.
In the gas industry the distance for this should be 300mm but if it is too close the problem can be overcome by using an open and shut extract terminal.
With oil this distance is 600mm and oftec will not sanction the use of the same terminal. HRM do not make a pluming kit either.
I'm resolved to having to move the boilers or vents but any ideas would be gratefully recieved.