Last May had a new Greenstar 4000 boiler fitted and only recently started using the heating. Once the set room temperature is reached the boiler modulates (presumably) and stays running for very long periods (many hours) but the circulating water is only luke warm (about 35 degrees) Any heating engineer would know that there is virtually no heat radiation at that lower temperature. I find this a great waste of gas and electricity and accomplishes very little. This may be the mode of operation that Worcester intended but they do not have to pay for the gas and electricity.
Question. I want to hard wire a conventual thermostat. Is this possible and what terminations do I use on the boiler control board? Any information, advice or suggestions would be much appreciated.
What controls do you have ?
What’s the boiler temp set to as the comfort II doesn’t adjust the flow temp
Do you have the hot water pre heat on ? Eg not eco ?
"Any heating engineer would know that there is virtually no heat radiation at that lower temperature"
They would also know that's one of the mechanisms used by controls with 'load compensation'. The thermostat tells the boiler to reduce the flow temperature when demand is low to reduce cycling. This form of control should save 3% of fuel compared with the type of on-off thermostat you are planning to replace it with. This is largely because the nice constant temperature allows you to set the thermostat to a lower average temperature than is needed with on-off control.
Thank you Chuck for your reply. I am aware of the so called 'comfort' mode but I cannot afford the luxury of a 'nice constant temperature'. That's ok if I'm sitting around all day doing little but if I am busy dashing around doing jobs etc or if I to go out for half a day etc I want to turn the heating down or off I expect boiler to turn off until I feel I want it warmer. I hate the idea of using gas and electricity (pump 96watt) besides wear on the pump (running continuously.) Same if a go away for a week or at night etc I want the house cooler. I've used a conventual on/off thermostat for the last 60 years without the slightest discomfort.
So, can a on/off thermostat be wired into the 4000? Thanks for your attention.
With respect, that is not the issue you described in post #1. Your complaint was that the boiler was supplying the small amount of heat required to maintain the setpoint, which is what a correctly working modern system should do and it will be more efficient than using an on-off thermostat.
In post #9 you've changed your complaint and now seem to be saying that, for example, if the room temperature is 20°C and you reduce the thermostat setpoint to 17°C the boiler continues to supply heat to radiators even though you actually want the room to cool. If this is the case, then there is an issue that needs to be sorted out. Things I would look at, in order are:
(a) The communication between the boiler and thermostat. Some systems (I'm not sure about yours) will have a 'safe mode' that runs the boiler at low power when there is a communication fault to guard against frost damage.
(b) The thermostat configuration of the themostat. Although it looks simple, the thermostat contains a 7-day event programmer that can change the setpoint up to 6 times a day for heating and 3 times for hot water. If you just turn the thermostat down manually, the setting will only stick until the next programmed 'event' overrides it. (The way round this is to activate 'party mode' for the length of time you want your manual setting to stick.)
(c) Reverse circulation causing activity in the hot water section of the system to warm radiators as a sided effect. This is usually a plumbing / installation error.
(d) Depending on how your system is plumbed, a stuck-open zone valve may be constantly demanding heat from the boiler. The thermostat can't shut the valve but can tell the boiler to supply minimum heat.
(e) An incorrectly set parameter in the thermostat, e.g. a minimum room temperature that is too high.
The above suggestions are based on my memory of how the Greenstar 4000 and Comfort+llRF usually work together so may or may not be applicable to your system.
Yes it can.
But my suggestion is you get the installer of the system back to address your concerns. Installers are supposed to make sure that the system is working correctly and that the customer understands the controls and how it should behave as the final part of the commissioning exercise. It is not uncommon for customers who have boilers installed in the summer to discover problems only when the weather gets colder.
Reply to Greenstar 4000 runs almost continually. Not good. in the Central Heating Forum area at PlumbersForums.net
Hi everyone, Just wanted to share my experience with "upgrading" an S plan setup to Opentherm and Vaillant Control Center (VR66). There are a few...
Hi Folks, I have a challenge with a Main Eco Elite 30 Combi which is short cycling on the CH. Water works fine. As soon as you have call for...
We are experiencing an issue with CH short cycling on a Worcester Bosch Greenstar 25i ErP boiler. From a cold start the boiler fires for only ~25...
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The...
Jaga radiators (with heat-exchangers) have their own small fans, that "will modulate down when the room temperature is met – the room temperature...