Discuss Help us understand how this UFH system works please! in the Water Underfloor Heating Advice area at PlumbersForums.net

How Underfloor Heating Works | John Guest Speedfit - https://www.johnguest.com/speedfit/underfloor-heating/underfloor-heating-explained/what-is-ufh/I[/URL] confess my background is electrics, not plumbing. What I don't understand is that the heat store appears to have only one coil, which takes incoming mains pressure cold water, heats it and feeds it to the taps. Apparently the UFH is connected to the same coil. Surely that means that water from your hot taps could be mixed with that running through the UFH pipes, unless there is some sort of hydraulic separation somewhere. It doesn't seem a very hygenic arrangement. I would be interested to hear others observations.
I hadn't , no. Cheers.
I confess my background is electrics, not plumbing. What I don't understand is that the heat store appears to have only one coil, which takes incoming mains pressure cold water, heats it and feeds it to the taps. Apparently the UFH is connected to the same coil. Surely that means that water from your hot taps could be mixed with that running through the UFH pipes, unless there is some sort of hydraulic separation somewhere. It doesn't seem a very hygenic arrangement. I would be interested to hear others observations.Sorry to ask again, but are you absolutely sure the UFH stops working if you turn the E7 off completely?
(probably not an experiment to do at this time of the year). The presence of the energy monitor is still bothering me🤔
The plot thickens😀
Communal heat-pump system heats Gateshead apartments
GOING GREEN IN GATESHEAD - DIMPLEX COMMUNAL HEAT PUMP SYSTEM WARMS APARTMENTS

" Heat meters in each apartment can be remotely read, so that each owner pays only for the energy they use"

This second article has this added text

"The nine LA 28 AS air source heat pumps are arranged in two separate banks and provide heat to all apartments, which are arranged in three blocks. The innovative solution was specified, designed and installed by Dimplex heat pump installer partner Azure Natural Energy Systems and was completed in late 2009. Matthew Evans, owner of Azure, explains: “We looked at all the alternative renewable heating systems available, including ground source heat pumps, water to water heat pumps using heat from the River Tyne, biomass and solar thermal combinations. The most cost-effective solution was this communal air source heat pump system to deliver heating to the buildings, with domestic hot water served by individual, electrically heated cylinders"
 
Last edited:
I hadn't , no. Cheers.

The plot thickens😀
Communal heat-pump system heats Gateshead apartments
GOING GREEN IN GATESHEAD - DIMPLEX COMMUNAL HEAT PUMP SYSTEM WARMS APARTMENTS

" Heat meters in each apartment can be remotely read, so that each owner pays only for the energy they use"

This second article has this added text

"The nine LA 28 AS air source heat pumps are arranged in two separate banks and provide heat to all apartments, which are arranged in three blocks. The innovative solution was specified, designed and installed by Dimplex heat pump installer partner Azure Natural Energy Systems and was completed in late 2009. Matthew Evans, owner of Azure, explains: “We looked at all the alternative renewable heating systems available, including ground source heat pumps, water to water heat pumps using heat from the River Tyne, biomass and solar thermal combinations. The most cost-effective solution was this communal air source heat pump system to deliver heating to the buildings, with domestic hot water served by individual, electrically heated cylinders"
I think you might have found the answer, in which case no need to pursue dual rate electricity!

Air source heat pumps don't provide a particularly high temperature at this time of year, so best to keep the UFH ticking over.

If timed night setback and control of individual room temperatures is appealing, suggest obtaining the chrono module and finding someone to install it. Otherwise just fiddle with the thermostats as required!
Best regards.
 
I think you might have found the answer, in which case no need to pursue dual rate electricity!

Air source heat pumps don't provide a particularly high temperature at this time of year, so best to keep the UFH ticking over.

If timed night setback and control of individual room temperatures is appealing, suggest obtaining the chrono module and finding someone to install it. Otherwise just fiddle with the thermostats as required!
Best regards.
I hope you don't think you're just going to disappear into the ether!
Thanks for the tip about keeping it ticking over.We've been wondering about how to use it most efficiently
I'm wondering how the billing works for a communal heating system because presumably it's not running off our meter?
Spotted a post on MSE forum that looked suspiciously like it might have been from a Friars Wharf resident. They were about the billing for the communal heating ASHP system for 85 flats. Guess what? The management company or building owner didn;t seem to know what they were doing. I don't think it's possible to work out how much each apartment has used. I bet there's been some interesting discussions at the residents meetings (if they have them)
 
I haven't disappeared yet, but please confirm we are talking about Friars Wharf, otherwise I'm going off at a tangent. No it's not running off your meter.

Here is a learned dissertation that just happens to mention how the Friars Wharf system, in general terms, is supposed to work, see page 113 figure 30 and beyond:
Doesn't really help us answer your burning questions.

It appears the bank of 8 air source heat pumps run from 3-phase 440v. I don't imagine they would try to measure the electricity consumed by each flat, only the total for the building per month/quarter etc. It is the purpose of the energy meter in each flat to determine, on the basis of the flow through the water pipe, the incoming water temperature, and probably the outgoing water temperature, what the kWh equivalent of energy used is. They then hopefully attribute the contribution of each flat according to the energy meter readings in proportion to the total consumption, so each pays their 'share'. No doubt with an admin/management fee on top. But still according to a transparent rationale that flat owners are aware of.
I believe the heat output of the heat pumps should be roughly 3 times the electricity they use.
So assuming the meters in the flats are actually accurate, the following things should be true:
1) adding up all the flat meter readings for a given period and dividing by 3 should total approx the electricity bill for the building for that period (actually this is the way to find out the exact proprtion)
2) dividing by 3 the unit price per kWh for the heat pump supply, and multiplying by the number of units used by a flat, should be the bill for that flat, and adding all the flat's contributions should pay the overall bill.
Maybe someone got their sums wrong, not all the heat pumps were working properly, not all the kWh meters were working properly, or some other part of Murphy's Law came into play, and the landlord was out of pocket.
Well that's my theory!
I hope they know what their doing with their bills now. I would hope the heating charges would be less than half the 'equivalent normal' electricity bill would be.

There should be information about this in the Management Pack, Handbook or "Safety Manual", or whatever they've chosen to call it, or the lease, or other documentation for the property. Normally you sign to agree to the terms.

Nice flats!
 
Last edited:
Whatsthenews, I've just discovered another thread on this forum on the same system, from 2010!
 
I haven't disappeared yet, but please confirm we are talking about Friars Wharf, otherwise I'm going off at a tangent. No it's not running off your meter.

Here is a learned dissertation that just happens to mention how the Friars Wharf system, in general terms, is supposed to work, see page 113 figure 30 and beyond:
Doesn't really help us answer your burning questions.

It appears the bank of 8 air source heat pumps run from 3-phase 440v. I don't imagine they would try to measure the electricity consumed by each flat, only the total for the building per month/quarter etc. It is the purpose of the energy meter in each flat to determine, on the basis of the flow through the water pipe, the incoming water temperature, and probably the outgoing water temperature, what the kWh equivalent of energy used is. They then hopefully attribute the contribution of each flat according to the energy meter readings in proportion to the total consumption, so each pays their 'share'. No doubt with an admin/management fee on top. But still according to a transparent rationale that flat owners are aware of.
I believe the heat output of the heat pumps should be roughly 3 times the electricity they use.
So assuming the meters in the flats are actually accurate, the following things should be true:
1) adding up all the flat meter readings for a given period and dividing by 3 should total approx the electricity bill for the building for that period (actually this is the way to find out the exact proprtion)
2) dividing by 3 the unit price per kWh for the heat pump supply, and multiplying by the number of units used by a flat, should be the bill for that flat, and adding all the flat's contributions should pay the overall bill.
Maybe someone got their sums wrong, not all the heat pumps were working properly, not all the kWh meters were working properly, or some other part of Murphy's Law came into play, and the landlord was out of pocket.
Well that's my theory!
I hope they know what their doing with their bills now. I would hope the heating charges would be less than half the 'equivalent normal' electricity bill would be.

There should be information about this in the Management Pack, Handbook or "Safety Manual", or whatever they've chosen to call it, or the lease, or other documentation for the property. Normally you sign to agree to the terms.

Nice flats!
Yes, we're talking about Friars Wharf, and I really appreciate your input Basher. I didn't think about looking for academic papers. The management company , Zenith, are Manchester based

Now in possession of a meter reading at least (although knowing what we now know about the ASHP's, I'm a little reluctant to accept their reading. Would rather have eyes on the meter myself.)
.
I agree with your calculations and the presence of the heat meter makes sense now, although we've never been told that we will need to submit any readings or that anyone will need access to look at it We are keeping a check on it.
Is it correct to say that in the coldest months (now!) the COP will be lower than 3?
My parents has a house with an ASHP (air to air) in the US when we lived there. Generally although the winters were much shorter and sunnier, we had colder temps than here and they had an emergency back up "heater" that came on automatically when the temp went down to below about -4c and the pump couldn't raise the air temp' sufficiently to reach the set temp'.
We don't have an info pack nor any instructions for anything.
We've emailed the letting agent and told them we think the UFH runs off communal ASHP and asked how it's billed.
Thanks again!🙂
 
Whatsthenews, I've just discovered another thread on this forum on the same system, from 2010!
Just had a reply to our email. Apparently the landlord pays for the UFH in with the service charges. I'll take a loom at the thread.
Thanks again for helping us with the conundrum.
 
Just had a reply to our email. Apparently the landlord pays for the UFH in with the service charges. I'll take a loom at the thread.
Thanks again for helping us with the conundrum.

Whatsthenews, I've just discovered another thread on this forum on the same system, from 2010!
yes, that's the same guy who posted in 2011 about the charges for the UFH (I posted the link a couple of posts ago). Doesn't sound like anyone knew what they were doing.
Sadly I can't see his photos. One guy states that the pump's in the wrong place!
 
Now in possession of a meter reading at least
i'm assuming you're talking here about the electricity supply to the flat, for hot water etc. Thats good news.
I hope the reading tallies reasonably with the last estimated bill! But of course that reading is nothing to do with the ASHP's and the UFH consumption.

As far as the UFH is concerned, the Rossweiner kWh meter should communicate readings back to a central unit. I believe all the flats readings would be logged centrally, or at least that would have been the case when the system was installed, probably integrated with some software that looks like nobody knew much about. Hopefully after all this time it's being done properly!

Thanks for the update. Hope things go smoothly at the flat.
 

Reply to Help us understand how this UFH system works please! in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator...
Replies
2
Views
139
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
441
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
553
Hi, I'm looking for a water pump to pump water from a storage tank at a constant 3 bar pressure. It's at a campsite I run that's at the bottom of...
Replies
2
Views
141

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock