Dear All,
Please kindly advise, i don't know what else to do! Had new boiler Vaillant 424 heat only open vent boiler installed with new flue and filter, new pump, plus new Hive. Did full power flush of all 5 radiators before the installation. It has been 10days and boiler stil not working properly. I tried to sum up points below, could someone kindly give an advise as the gas engineer now says he doesn't know what to do and do not wan to refund so i can call someone else. I just bought this house as my first home and money very tight.
1. Boiler comes on if i set Hive to 26C and will work fine (max it reaches temperature of 24 so always stays on).
2. As soon as i lower temperature to 22 for example, the boiler will power down but will never come back up to maintain target room temperature, it will keep dropping down to 17C (I'm at work from 6am to 6pm so watching Hive on the phone).
3. Fault 23 comes back on every time i lower the temperature - the boiler will fire up but will stay on only for half hour or so.
4. Pump makes plenty of crackling noise on occasion, gas engineer was sure its air in the system so all radiators has been bled and system refilled a few times.
5. Vaillant advised Fault 23 related to flow and return temperature, gas engineer says he adjusts flow and return every time he comes in but boiler still will not come on to maintain set target temperature.
6. For me to turn it back on i need to first close all the radiators expect for one closest to the boiler and let it heat, then i start to open other radiators, if i restart boiler after the fault with all the radiators open the boiler will not stay on and fault message returns after a few min.
7. Hot Water works absolutely fine, it turns on from Hive and heats up no problem, i hardy have it on as I'm on my own so just an hour daily or 3 hours during weekend days.
Please could someone help me figure this out, i can't take any more days off at work to keep getting the gas engineer in and every time he leaves same issue comes back. Any other details you need please just ask i will do my best to answer.
Thank you very much!
F23 fault means the boiler flow/return temperature is >35C so probably air still in the system or pump speed too high drawing in air through the vent pipe possibly due to blockage where the cold feed joins the vent.
Can you post the boiler model, the exact pump model and mode/settings, (a photo of the pump LEDs etc while running will help) and a photo of where the cold feed and vent are tied in.
Thank you for your reply! I will get all the details you mentioned. Yesterday he checked flow and return temperature and it was 36C and 38C. He then called vailiant and they mentioned that boiler settings should not be on 24Kwh but should be on Auto, so he changed that and lowered pump speed to 2 (Grundfos UPS3). The pump still makes crackling noise but much less as i bled radiators again, but seems like air just getting in regardless how many times i bleed them. I set target temperature on Hive at 21 so will watch today if it maintains thought out the day, if not then what he changed yesterday did not helped and the boiler did not stayed on.
Thank you for your reply! i can check on details you mentioned. The flow/return yesterday showed 36C and 38C. He spoke to vailiant again and they mentioned that he should only set boiler to Auto rather then 24Kwh that he did, so that was changed, the pump itself Grundfos UPS3 15-50/65 230V stil makes noise but less loud as i bled radiators again yesterday, a little air did came out. He also lowered pump speed to 2. When i left today i set target temperature to 21 so will be able to see if boiler stayed on during the day, if tempreature will just keep droping then i know i will return to Fault 23 again.
Are you saying that the return temperature is varying between 36C and 38C?, if so the flow temp must be 71C to 73C if its flagging F23 (dT 35C).
The UPS3 is a very powerful pump and IMO will create havoc on most vented systems as it will pump at a constant 6.4M head on speed3 and cause air ingress through the vent, even speed 2 at 5.2M can be excessive, I would suggest changing to (constant pressure) CP2 where the pump will run at a constant 3M head or/and try proportional pressure PP2 which starts at 3.75M head but modulates the speed to run at a even lower head of probably ~ 2.5M with 5 rads, you can try both modes yourself, its only a few button presses, continue to vent air, you could also hold a "glass" of water with the vent end immersed in it and see what happens to the level.
the exact numbers they mentioned were D40 at 38C and D41 at 36C, sorry i should have wrote that, im strangling with understanding to be honest. These temperatures were after about an hour he worked on the boiler so vailliant said he needs to start again from cold system. I will do pictures today so you able to see/understand better the pipe work and will include whats on boiler display. Thank you very much for looking into this in detail.
I think auto and 24kw settings are far too high for a 5 rad system, probably better with 10 - 12kw.
Thank you for your reply! Could i please ask is this possible to do on this new boiler? The boiler i had previously was 16 years old but also 24Kw so i did like for like change. Is it possible for me to change the setting from Auto to 10/12kw or do you mean i need to get a different boiler with lower Kw?
Change d.00 max setting to 10 (kw) or so.
Also see if d.05 (boiler flow temperature) is settable, it states below that it isnt which seems strange, also note the anti cycling time, d.02.
Amazing that the flow/return temps are 38/36C, boiler firing??.
There is a d setting in some of these boilers where you can control the return temperature, it might be in one of the d codes if selected.
When f23 was flagged what did d.40 & d.41 read?.
You’re welcome. No, i don’t mean swap the boiler. As above, it’s possible to range the heating side down, and shouldn’t affect the hot water delivery - let’s face it, there’s nothing to lose by trying it. I take it you missed my earlier post regarding the motorised valve?
Will defiantly try it! Sorry, regarding motorised valves - both were checked and seem to work ok. Always responded even with previouse old boiler so i asked the gas engeener if i should order new ones as we upgrading the system but he was sure they work well still.
Update- Same Fault 23 was on the boiler when I got in, I have closed 4 radiators and restarted the boiler, it only keep working if I open the rest of the radiators one by one after they got hot. Temperature on display keeps going up and down and radiator sign keeps flashing. Gas engineer coming back tomorrow to start again, is there anything else I need to tell him? ( I printed all your previous replies for him).
Thank you!
Irina
Check the (downward) vertical pipe from the ABV (automatic balancing valve) is cold/cool with boiler running, it looks as if its set to max (ie closed) index of 0.5, 5M. It looks suspiciously as if its teed in to where the cold feed traditionally is/should be, alongside the Vent, if not a combined vent and cold feed, like mine. Try and see where the cold feed pipe is teed into the system it will be a 15mm pipe coming from the side (bottom) of the F&E tank, also check the obvious, that this tank contains water.
This is how it should be piped it's obvious that the existing pipe has been adapted and only minor alterations made it not the best job in all honesty , we need to know where the vent and cold feed are connected ? If it's on the live side of the pump ? It could cause issues ? Kop
My water tank is in the loft - is that what you mean by cold feed connections? (apologies im not very knowledgeable in this)
Vent is on the side of the house, sticking out from the wall.
No the heating system cold feed and vent connected into the system pipework?? As the picture below
Can you post a photo of the very top of the boiler where the flow & return pipes are or/and ask you plumber to ensure that the flow pipe is connected to the pump inlet.
Edit: As per post#14.
Will do, sorry I didn’t thought of it. He is coming today at 4 to start, I got all the previous messages ready. He installed it on 10th March so it’s been a while and I really hope with all this help here he will be able to fix it.
Is there only one tank in the loft?? or are there two, one much larger than the other??.
It looks like you may have a sealed system and a system boiler, not a heat only boiler, which I think refers to a vented system, you should see a red tank somewhere, probably near the boiler that may have a pressure gauge on it or the boiler may show a indication of pressure like 1bar to 1.5bar or similar?.
Should definitely be Heat only as I specifically wanted like for like change, please see a few pics with boiler details. Plumber would have noticed that’s it was s y stem one I hope, I’m doubting everything now :(
The attic Tank may be your F&E tank for the boiler/system and you may have a unvented HW cylinder fed with mains cold water, if the hot water pressure/flow is the same as the cold water kitchen tap then probablay a unvented or look at the label on it, it should show the pressure.
Reply to Help with New Vaillant Boiler not staying on in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net
I have a Worcester Bosch Greenstar 15i condenser boiler which is about 13 years old. There is a separate hot water tank. Recently the fan in the...
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
MartinPod81
M
Would like some help please as my Drayton Wiser system is a mess. I had 2 TRVs in the lounge, one in the main bedroom, the rest of the house - 6...
I have a Vaillant eco plus 837, year installed 2008. It works well. We have one large zone for the house with 13 rads running off it. We also...
Hello, We had an extension built seven years ago. Initially the builders' plumber connected the heating to the house system but this didn't work...