Would a diverter not making cause lockout though? 🤔

Not sensing pump is spinning it’s a pump proving like the vaillants using the pressure sensor to check there’s an increase when the pump is on
 
Not sensing pump is spinning it’s a pump proving like the vaillants using the pressure sensor to check there’s an increase when the pump is on
Hi,

Come back here this morning turned heating on and pin still did not come out to make connection to pump proving switch. I made manual contact to switch and the burner ignited. Boiler ran for around 2-3 mins and then burner cut out and flame failure started flashing again.

Does it seem to be an issue with the pump. I am getting 230v at pump.
 
Hi Guys,

So replaced pump and both dhw and pump proving heating diagphrams.

The back pump proving pin still won't come out to make contact with the switch.

However if I make manual contact to switch burner fires up both on ch and hw.

Could it be a faulty diverter valve.
 
Also check the little 4-6mm pigs tail tube
 