Like Harvest said around £200 on Amazon ... I wouldn't be without mine now, i've now had 3 commercial UFH jobs sorting out systems that others have "commissioned " had one where there was a 240v actuator on a 24v system, the commissioning certificate had a flow Rate written on it! .... i'd like to know where they got that reading from ... i use mine to show the customer when I'm commissioning, they like seeing the loops heating up in the floor
 
It's not heating season, so the only demand on the primaries at this time of year, in your average household (correct me if this is not the case and the users are foreign) should be for hot water and reverse circulation would occur if the cylinder is not the last T on the boiler return, thus allowing hot primary return from the cylinder to find its way into the heating circuits.
 
It's not heating season, so the only demand on the primaries at this time of year, in your average household (correct me if this is not the case and the users are foreign) should be for hot water and reverse circulation would occur if the cylinder is not the last T on the boiler return, thus allowing hot primary return from the cylinder to find its way into the heating circuits.
All of the returns now have non returns on them.
 
All of the returns now have non returns on them.

Ok. Then it has to be a wiring issue and primary HW flow is getting to heating circuits via a mzv that is open when it shouldn't be... have you checked for this? Can you confirm that the problem occurs when there is a demand for HW only?
 
I do like your thinking. But It does not happen when the hot water is on. Only when the UFH is switched on?
 
I do like your thinking. But It does not happen when the hot water is on. Only when the UFH is switched on?

Ok. Now getting more of the story which is probably in the previous posts but that's easy to miss until one joins the party;)
If this only happens on demand for UFH then what is the mzv for the rad curcuit doing at that call? Does it open up? Check wiring to it from stat(s) is there a backfeed that is energising it?
Maybe it's faulty and staying open. I'd isolate it electrically from the circuit and then fault find on it if the problem goes away during isolation.
 
Ok. Now getting more of the story which is probably in the previous posts but that's easy to miss until one joins the party;)
If this only happens on demand for UFH then what is the mzv for the rad curcuit doing at that call? Does it open up? Check wiring to it from stat(s) is there a backfeed that is energising it?
Maybe it's faulty and staying open. I'd isolate it electrically from the circuit and then fault find on it if the problem goes away during isolation.
The heating circuit MZV is brand new. I fitted a new one from the suppliers incase the old one was temperamental and no power to the valve when UFH is on at all not even the 50/75volts you sometimes get when they are back feeding.
 
I recently had to use TI to locate my son's corn snake which had escaped in the car on the way back from the reptile shop he works at :)
 
So, not had chance to buy a TI as yet as so busy. But popped back to this job yesterday. To take a more in depth look. So I have some pictures and I known it is a mess but just after a bit of advice as UFH is NOT MY THING. If you think it is better for me to pass onto an UFH Engineer I will do so. Quick update all rads eventually come on with the UFH 2 port open. But not when the hot water 2 port is open.

IMG_9680.JPG


IMG_9681.JPG


IMG_9682.JPG


IMG_9684.JPG


IMG_9685.JPG


IMG_9686.JPG


IMG_9687.JPG


IMG_9688.JPG


IMG_9689.PNG
 
They haven't used an old feed from a rad to heat the underfloor/ supply the manifold have they?
 
But that wouldnt explain why it has only just starting to do it. The owners is adamant that they used the UFH more then the heating and it defo didn't do it before?
 
Heating two port been replaced?
 
so the heating doesnt come on with the hot water at all?
 
No mate the hot water 2 port is perm open as is a thermal store. Rad cold when water only is on
 
No idea but presumed it was as the hot water two port was perm open with no timer.
 
To be honest I thought it was a normal unvented but when I said to a work mate the 2 port was open all the time when there was 240v present he was the one that said thermal store so I went with it.
 
That's what I thought but my G3 knowledge is tiny

TBH I would get the underfloor up and running and get it into fault state and see if the other side of the valve is hot if it is close the valve and do the rads cool etc
 
I have tried that also mate and turned off the temp valve to min on the UFH valve and they still get hot. I have noticed that the pump for the UFH is on the flow though if that makes a difference?
 
Status
Not open for further replies.

Reply to NO I AM NOT AN UNDERFLOOR HEATING EXPERT! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
308
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably no need for me to needlessly heat hot water. My intention was to turn the boiler off along with the mains water when going away. Now, I have heard...
Replies
1
Views
99
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
226
P
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
207
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...