Currently having an issue I can't figure out and could do with maybe some pointers from some of the more experienced members on here. Standing pressure at meter is 22.9 mbar and working pressure in 21.8mbar at inlet to boiler working pressure drops to 10mbar. It's a short pipe run so undersized pipework is definitely not the cause. All visible pipework appears undamaged as well. What could cause such a large pressure drop across say 5m of gas pipe? Property has been vacant for a few months and unused if that makes any difference. Any suggestions would be appreciated
 
Get the networks out to check the regulator
 
It's an old baxi bermuda bbu. Taking inlet pressure off the inlet at gas valve and also off the gas fire in front of it. Yes I'm gas safe, newly qualified.
 
Working pressure is fine at the meter though just by the time it gets to an old bbu it's dropped to 10mbar at the inlet to the gas valve

You have to understand the difference and interaction between flow and pressure. If you have enough standing pressure, but it drops too much when wotking, you do not have enough flow. You have been given the probable answers above, faulty regulator or problem with the main. Think of it as, when the boiler fires, it uses gas, which must be replaced by the same amount of gas flowing in from the main to replace it, or there will be less gas in the pipe. Less gas = less pressure. Slow flowing gas will still build up pressure when it is not being used.
 
I had the same issue once on an install of a replacement boiler. Contacted the gas supplier who changed the regulator and problem solved.
 
If you got 21mb working pressure at meter but 10mb at appliance ...how is that a faulty regulator?
 
Where are you measuring the 10mbar working pressure on the gas valve ? Rigbt or left test point . Kop

Screenshot_20181215-061015_Drive.jpg
 
hello all , i am also a newby but have 40 years in refrigeration and a/c . would it be safe to say , have you checked the pressure at the meter when app is running as well , and if it is acceptable then it is either the regulator , pipe damage/blockage ?
 
Last edited:
hello all , i am also a newby but have 40 years in refrigeration and a/c . would it be safe to say , have you checked the pressure at the meter when app is running as well , and if it is acceptable then it is either the regulator , pipe damage/blockage ?

Gofo, if he has 21mb working pressure at meter it cant be the regulator...the regulator is upstream of the meter test nipple.

Assuming hes not taking a burner pressure reading its either a blockage or GV to blame
 
Status
Not open for further replies.

Reply to Pressure drop across gas pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Non-professional / knowledgeable person here. I'm a Brit in Romania who volunteers for a charity building an old peoples home for needy old...
Replies
3
Views
423
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
408
I have an Ariston combi e on lpg, the gas pressure drops from a lovely 37mb to 0 the second gas valve opens and fan starts to run, usually would...
Replies
13
Views
1K
Hi I've got water hammer issues with my cold feed and some with the hot feed. When the cold sink tap, cold bath tap and thermostatic shower in...
Replies
1
Views
458
Hi everyone.! I have a Betacom 2 24 Boiler ( 10 years old) and have been having issues with the pressure dropping. So far, I have had 2...
Replies
2
Views
864
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock