I have a job where I need to run 30 metres of 28 mm and 10 metres of 22mm copper tube. Now there is no gas hob in the place so I need to light the gas while purging. What right do you guys make up in this scenario. Cheers
Discuss Purging long gas supply in the Plumbing Jobs | The Job-board area at PlumbersForums.net
Almost right. :yes:
Went wrong by adding the meter before adding your 10%.
that size is the iv of your result/size over 35m of 22mm
True, as that is minimum purge vol but I want to check whether I was taught wrong about the multiplying by 1.5?
Now that's a funny thing. When I first did ACS, I was taught to do your method. Subsequently I was taught to add meter volume first and then add 10%.
Some acs centres have their heads up their rses.
Gimme a minute and i'll post a pic from UP1B.
looking at same volumeaccording to this app (uk gas app) with a g4 meter with straight run of 35mx22mm pipe with no fittings comes to 0.0305m3 so a 30m run of 28mm and 10m of 22mm with 6 fittings cant equate to the same?
Just checked the Construction Skills textbook. 10% added to pipework and then meter volume added. So yeah, the worksheet the assessment centre gave us was wrong!
Although, I noticed something else in the book - we've all been adding 0.008m3 as meter volume, but that is meter internal volume. Meter purge volume is given as 0.01m3 for U6/G4.
God, I'm sad...
Yip. For standard G4/E6 upto 28mm pipe the standard purge is 0.01.Just checked the Construction Skills textbook. 10% added to pipework and then meter volume added. So yeah, the worksheet the assessment centre gave us was wrong!
Although, I noticed something else in the book - we've all been adding 0.008m3 as meter volume, but that is meter internal volume. Meter purge volume is given as 0.01m3 for U6/G4.
God, I'm sad...
Meter purge volume is given as 0.01m3 for U6/G4.
Yip. For standard G4/E6 upto 28mm pipe the standard purge is 0.01.
Bigger meter and or greater than 28mm pipe then you need to calculate.
Wow.a lot of info in there guys. Thank you. So basically, all I need to do is purge 0.01 and all is well as no 35mm pipe or u16 meter.
So I am within scope.
I know some boilers have a purge setting on them so think I shall do it this way
Thanks for all the help guys. I appreciate it.