Hi I have conected a small rad with 15mm pipe fed from 10mm system there is no air in the read water is coming out no bubbles but rad don't get warm the rad its conected to dos get hot the 15mm pipes have to go up and over a small door and back down to the new rad what am I doing rong please
 
You can’t tee of 10mm for another rad eg 10mm won’t do two rads
 
Although as Shaun mentioned, 10mm is no good for 2 rads. You should still be able to get some heat.

Have you got bleed nipples on the highest point above door? There has to be air in there stopping circulation.

Close all rad valves and open the valves on problem rad one at a time and bleed water out until warm. That’s your best chance without high point bleeds.
 

Reply to Rad not geting warm but no air in rad in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi thank you for letting me join this forum . We have an air to water heat pump but the bungalow is piped in micro bore 10mm pipe which doesn’t...
Replies
4
Views
364
About 5 year ago, I had a new central heating system (radiators) installed to replace my old warm air underfloor system. The warm air side of the...
Replies
5
Views
440
I have Honeywell Valencia TRVs 10mm pipe size, I’m making mods to accommodate larger rads and it looks like the 10mm compression insert is special...
Replies
7
Views
712
Hoping somebody can help, So, in a nutshell… Standard 90s Westbury home – condensing boiler, pump, wall thermostat, etc etc... Normal, common or...
Replies
8
Views
597
Sorry I have sort of asked this before, tried professionals but not great 1st experience hence DIY attempt attempt again. 2 completely cold...
Replies
3
Views
668
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock