D

donkeeboy

Hi guys,

I had a Worcester bosch engineer out yesterday to look at my boiler, its been giving me some gip.

Turns out I need to replace CH pump, however during the work guy did a gas pressure test and said it was too low. Now my boiler cover plan from Worcester bosch is invalidated until I get the gas pressure sorted.

It was 13.3 at the boiler - and then 13.1 when the gas hob was going full blast. I have no other gas appliances. I need to have 16.5 at the boiler.

Then I got natrional grid out to test meter, as they changed it abut 6 months ago and I recalled the guy saying pressure was a bit on the low side when he changed it. The pressure at the meter was 21. He adjusted it a bit and said he cranked it up to 22 last night.

I just looked at the pipe work from the mains inlet, to the boiler. There is 0.5 metre 22mm copper coming out meter, then 0.5m 1.25" iron pipe, then 3m 1" iron, then the rest is 12 metres of 22mm copper all the way to boiler. 16 metres pipe work in all.

I counted the elbows, I got 22 elbows between the meter and the boiler. The engineer said yesterday you lose x amount of pressuure per elbow. Cant rememebr the amount, maybe he said up to 0.5 per elbow.

Anyonen got any views? I am losing a lot of pressure somwhere - got no leaks! With that amount of elbows, does it sound about normal to lose that amount of pressure? (22 down to 13.3)

Obv this aint the kind of thing I can sort myself, it's gas, would just like to hear some opinions so I can have some confidence in whats require to sort it out.

Thanks very much guys.
 
Last edited by a moderator:
why have you got so many tees ? have you got 22 gas appliances ?
 
Oh crap - when I said tee's I meant elbows! LOL Sorry guys!

So 22 elbows - i just have the boiler and gas hob running on gas.

Just updated my OP to say elbow not tee to avoid any confusion
 
Last edited by a moderator:
Firstly it sounds like a very poor install with so many elbows.
Did the Nat grid guy test the working pressure at meter? From your post it sounds like he has just upped the standing pressure by 1 mbar which is not getting you anywhere.
By sound of it you will either need the supply pipe from meter to boiler re-run or have the meter cranked up to a standing pressure of 25 or 26 mbar to give you the gas.
 
Thanks Graham.

Yeah the boiler was installed 3 years ago by corgi guy, the gas pipe from meter is the original one from before, he just changed the bit at end near boiler.

I suspect your right about the nat grid guy. i was not here as he came last night instead of this morn as planned, I guess he just upped the standard pressuure as you say. That extra one mbar aint gonna help your right.

So is this all down to the nuumber of elbows do youu reckon?

Im sure some can be removed but not all that many to be honest, its a tricky run to the boiler in an unusual property.
 
When the boiler was installed the gas pipe should have been checked to make sure it was big enough for all your gas appliances.A calculation should be done to determine what size pipe you need. It sounds like that wasn't done which would mean the boiler has never had an adequate gas supply. Bad installation if that's the case but nothing unusual I'm afraid,there are a lot of "boiler swappers" out there.

Find a good Gas Safe engineer to check and uprate your gas supply,it probably needs to 28mm most of the way.
 
Last edited by a moderator:
Aye, a nice big juicy length of 28mm and as few bends as possible.
 
OK gents, thanks for your advice.

If there's any gas safe guy's on here in Leicester who wants to do this for me let me know.
 
28mm i have had to go as far as 1 1/4 once many years ago sadly inlet was 20 but the boiler was a Bahama hard to change it for a 105 then when it died LOL
 
When the boiler was installed the gas pipe should have been checked to make sure it was big enough for all your gas appliances.A calculation should be done to determine what size pipe you need. It sounds like that wasn't done which would mean the boiler has never had an adequate gas supply. Bad installation if that's the case but nothing unusual I'm afraid,there are a lot of "boiler swappers" out there.


Agree with all of above.


Find a good Gas Safe engineer to check and uprate your gas supply,it probably needs to 28mm most of the way.

And this bit to !
 
Status
Not open for further replies.

Reply to Significant drop in gas pressure between meter and boiler in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Non-professional / knowledgeable person here. I'm a Brit in Romania who volunteers for a charity building an old peoples home for needy old...
Replies
3
Views
407
Had conventional boiler and tanks removed last year and new combi fitted and just recently had it serviced but the guy who did it has given me a...
Replies
9
Views
774
M
Hi, we have a back combi heater. Whenever the heating comes on it seems to lose pressure within a few hours and I have to refill each morning...
Replies
1
Views
403
Hi, I am a homeowner but caught between a rock & a hard place. I am trying to get a Vaillant ecoTEC 630 plus serviced but the gas safe engineer &...
Replies
8
Views
1K
I had a boiler check today all went well, and then he went to check on the gas meter which is in my larder in the kitchen high up on the wall...
Replies
1
Views
683

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock