Hi first time post,

Got called out on a Sunday regarding a boiler breakdown.
Previous day both electric and gas meters had been changed to smart meters and the boiler had been deemed AR as the pilot would light (electronic ignition) but main burner failed to light.
Inspected the boiler (glow-worm). All OK other than the need of a bit of a clean.
Still would not spring into life.
Then checked the power into boiler, 240 volts on the neutral which made me suspicious so fetched from the van a socket tester and found 3 other sockets around house reversed too. (reverse polarity affects flame rectification).
Called power emergency out and they came out within 30 mins and proved my suspicions correct that cables in meter box were reversed. He could not swap the cables round in the meter box as this holds him liable for any damage the reverse polarity may have caused so pulled the main fuse.He told me this was a serous issue and installer could be looking for a new job Monday morning.
The energy supplier came back later that evening and rectified the fault.
Not a common problem but might help someone else in future who reads this.

K. Miller Gas Safe ***91
 
Seen it all

Gas meters without seals copper showing out of the meters etc doesn't surprise me they get given a min of 6 a day to do
 

Reply to Smart Meter install and boiler breakdown. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
324

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock