Looks that way all right but a bit strange that with HW only selected that the cylinder temperature doesn't continue rise, if the zone valve is passing it can only mean that the HW programmed on time is spot on and shuts the boiler down or the CH comes on shortly afterwards.
Might be worth extending the HW on time and letting the CH off until/if the cylinder continues heating.

Probably no good though because boiler will shut down anyway once SP temp is reached on HW only.
 
Last edited:
Thanks again for your help. Having got hold of a thermometer, I was wrong about the water being hotter than before when the pressure reading was higher.

I have since discovered that the pressure gauge is attached to a tiny pressure reducing valve between the cylinder and a shower I don't often use. The gauge is just after this valve and before the shower. There was some trapped air in this part of the pipe which was causing havoc. I think the trapped air was being heated due to the pipe in question being close to a very hot central heating pipe under the floor somewhere. The expanding air may have increased the pressure in that section of the pipe where the gauge was. The pressure reducing valve was stuck closed, not allowing any backflow when other hot water taps were turned on. Letting hot water out of that shower seems to have displaced the trapped air and sorted things for now.
 

Reply to Unvented cylinder won't stop heating up when CH is turned on in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
501
losing pressure
L
Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or...
Replies
0
Views
605
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably...
Replies
1
Views
167
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
444
T
Hi We urgently need to get our h/w cylinder replaced because it's leaking. Our current system is oil boiler feeding underfloor downstairs...
Replies
2
Views
403

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock